Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84564members
353833posts

ClearSCADA - GeoSCADA Tune Limit function

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
SCADAPro52
Ensign
Ensign
0 Likes
3
1570

ClearSCADA - GeoSCADA Tune Limit function

We would like to use the Tune Limit function in our system but limit it to only the High and Low alarm points.  Is there a way to limit the availability of the limits to the Controller?  Also would be attractive to be able to define limits for the tuning range as well.

Anybody aware of this capability? 

45+ years in SCADA & ICS and still learning every day!

Accepted Solutions
tfranklin
Lt. Commander
Lt. Commander
0 Likes
0
1562

Re: ClearSCADA - GeoSCADA Tune Limit function

We've currently do something like this in our systems, but to my knowledge it has to be scripted.  You'd create a form for user input for a high/low value, you can even pull in the current acceptable ranges to the form and show them as static text.  Have some checkboxes for enabled/disabled, etc..

 

Once the user hits OK, you'd commit the changes.  It's a workaround, but I'm fairly certain it's the only workaround. 

See Answer In Context

Tags (2)
Jimi
Commander Commander
Commander
0 Likes
1
1553

Re: ClearSCADA - GeoSCADA Tune Limit function

When using a SCADAPack E in combination with GeoSCADA (ClearSCADA), this is a fully integrated feature.

1, You'd need to create a SCADAPack E type object

2, after configuration right click on the object in the DB view & you'll see all of the available config options

Global Training Manager
SCADA & Telemetry

See Answer In Context

3 Replies 3
tfranklin
Lt. Commander
Lt. Commander
0 Likes
0
1563

Re: ClearSCADA - GeoSCADA Tune Limit function

We've currently do something like this in our systems, but to my knowledge it has to be scripted.  You'd create a form for user input for a high/low value, you can even pull in the current acceptable ranges to the form and show them as static text.  Have some checkboxes for enabled/disabled, etc..

 

Once the user hits OK, you'd commit the changes.  It's a workaround, but I'm fairly certain it's the only workaround. 

Tags (2)
Jimi
Commander Commander
Commander
0 Likes
1
1554

Re: ClearSCADA - GeoSCADA Tune Limit function

When using a SCADAPack E in combination with GeoSCADA (ClearSCADA), this is a fully integrated feature.

1, You'd need to create a SCADAPack E type object

2, after configuration right click on the object in the DB view & you'll see all of the available config options

Global Training Manager
SCADA & Telemetry
BevanWeiss
Spock
Spock
0 Likes
0
1510

Re: ClearSCADA - GeoSCADA Tune Limit function

@Jimi The Tune Limits is a built in capability of the SCADAPack DNP3 Points, but restricting which limits can be tuned is not.

And there is not a way to restrict what the values for the tune limits can be (apart from being within Underrange/Overrange).

 

I think what the OP is after is a way to restrict the High Tuned Limit to be within some range (such as 150-250) whilst the Low Tuned Limit could only be in another range (like 25-50).. with the Underrange and Overrange still set as required at 0 and 1000.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..