Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Call built-in Interval Control as a user Pick Action

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: Call built-in Interval Control as a user Pick Action
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Janeway sbeadle Janeway
217
BevanWeiss
Spock BevanWeiss
81
AndrewScott
Captain AndrewScott
54
AdamWoodland
Commander AdamWoodland Commander
23
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
rlao
Lieutenant rlao
Lieutenant

Posted: ‎2020-01-14 10:20 PM . Last Modified: ‎2023-05-03 12:19 AM

0 Likes
4
1672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-01-14 10:20 PM . Last Modified: ‎2023-05-03 12:19 AM

Call built-in Interval Control as a user Pick Action

Hi,

 

When configuring fields such as alarm redirection delays and execution offsets (time-based interval properties) in a database object's properties, it brings up a nice Interval control popup that lets you explicitly specify number of hours, minutes, seconds, etc. which makes configuration very intuitive.

 

However, when you call a control method on those types of properties as a pick action for example, you don't get that nice interval control popup. You just get a generic control dialog box and you are forced to input your desired interval as number of seconds.

 

Is there a way to call that nice Interval control as a user method so I can put it into a mimic script?

Labels
  • Labels:
  • SCADA
  • Telemetry
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-01-15 10:47 PM

0 Likes
3
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-01-15 10:47 PM

There is no way that I know of to do this.

 

In the past we've always had to create a VB form to allow for such 'complex' data entry.

It might warrant a feature request however.  I'm just not sure how it could be exposed.  The ?Control action really attaches to an entire point object.  I guess there could possibly be a ?Configure:'PropertyName' action exposed which would call up the appropriate custom dialog for the PropertyName specified.  Aggregates could be handled with

?Configure:'AggregateName.PropertyName'

 

But again, I don't believe anything like this is currently available within ClearSCADA.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply
Replies 4
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-01-15 10:47 PM

0 Likes
3
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-01-15 10:47 PM

There is no way that I know of to do this.

 

In the past we've always had to create a VB form to allow for such 'complex' data entry.

It might warrant a feature request however.  I'm just not sure how it could be exposed.  The ?Control action really attaches to an entire point object.  I guess there could possibly be a ?Configure:'PropertyName' action exposed which would call up the appropriate custom dialog for the PropertyName specified.  Aggregates could be handled with

?Configure:'AggregateName.PropertyName'

 

But again, I don't believe anything like this is currently available within ClearSCADA.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-01-15 11:01 PM

In response to BevanWeiss
0 Likes
1
1654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-01-15 11:01 PM

Immediately after I posted the reply I thought of a way that 'might' have worked.  But I just tested it and it didn't.  So you can strike out this option.

 

If you call a Logic Program which has VAR_INPUT parameters configured, put don't specify them when executing (through a UI control), it will prompt you to enter the parameter value.  I was hoping that having a TIME VAR_INPUT it would prompt in a fashion that allowed for entering of time duration, which could then be scaled into the appropriate property value.  Unfortunately this was not the case, and it only provided a simple text entry field (which I'll raise a feature request to try to enhance).

 

So there's no working option I can recommend sorry.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
tfranklin
Lt. Commander tfranklin
Lt. Commander

Posted: ‎2020-01-16 05:53 AM

In response to BevanWeiss
0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-01-16 05:53 AM

We've requested this feature a number if times in the past.  My first thought was to have them utilize the DisplayObjectMenu function call and add an option for something like &ControlOnly=TRUE to the end.  DisplayObjectMenu accesses the entirety of the object similar to the ?Control function would. 

 

We've tried using DisplayObjectMenu and excluding everything but control, but since there are other items in that "Group" of exclusions it ultimately still prompts you to select something prior to getting the control menu. 

 

To those who roam the forums about, please consider this feature in future releases.  As Bevan mentioned, the only suitable workaround is to script a form that is somewhat complex due to consideration of varying datatypes and error handling with control min/max. 

  • Tags:
  • control
  • forms
  • pick action
Reply
rlao
Lieutenant rlao
Lieutenant

Posted: ‎2020-01-16 03:15 PM

In response to BevanWeiss
0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-01-16 03:15 PM

Thanks bevan, I feared this might have been the case. Looks like I'll just have to script a user form myself

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc