Power Meter connected to PAS800 does not sample data on Energy Hub

EcoStruxure Energy Hub

This forum is dedicated to supporting EcoStruxure Energy Hub service providers and partners with system implementation, reporting skills growth, and in demonstrating profitable improvements in monitored sites. Ask questions, get expert answers and the latest offer news, provide feedback and share community experience and knowledge!

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • EcoStruxure Energy Hub
  • Power Meter connected to PAS800 does not sample data on Energy Hub
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thierry_Baudard
Commander Thierry_Baudard Commander
8
EduardoFainblum
Commander EduardoFainblum Commander
6
Mathew_Losey
Lt. Commander Mathew_Losey Lt. Commander
5
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server
product field
Schneider Electric
PowerLogic PM5000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Energy Hub
Start a Topic
vihanger
Ensign vihanger
Ensign

Posted: ‎2024-09-25 03:01 AM

0 Likes
3
1006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-25 03:01 AM

Power Meter connected to PAS800 does not sample data on Energy Hub

I have connected a setup with a PM5560 power meter connected to a PAS800 power meter. Data sampling and cloud service are enabled in the panel server.

 

Screenshot 2024-09-25 151621.png

 

When logged into the energy hub, the panel server has not sampled any data.

 

Screenshot 2024-09-25 151858.png

Screenshot 2024-09-25 152201.png

 

 

Labels
  • Labels:
  • Knowledge Base
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2024-09-26 03:26 AM

1 Like
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 03:26 AM

Hello @vihanger ,

 

Based on the Panel Server (PaS) screenshot, everything seem to be correct in the field:

  - The measurements  are correctly collected by the PaS

  - The green indicator "cloud services" in top rigth corner  is green to indicate that the PaS is connected to SE cloud.

 

Next  checking is now in EEH web portal>Setup> communication to verify if the PaS is viewed as connected in EEH (picture herunder)

 

 

Last but not least, a frequent issue is to not wait enough time before checking data in EEH (may be your case?). First collected Data are available in the INVESIGATE> ASSET view in trends after 10 minutes (PaS publictaion period).=> screenshot1 hereunder

 

Thierry_Baudard_0-1727345935965.png

 

Your commissioning experience is very interesting for the EEH community so please keep us informed if you solve the problem,   if my post help you to solve the issue, etc...

if no: we will switch to SE  support team to help you.

if yes, you can mark this topic as a solution for all of us

 

Thanks for your post

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply

Link copied. Please paste this link to share this article on your social media post.

Dave_Trenaman
Lieutenant JG Dave_Trenaman Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-26 07:50 AM

1 Like
0
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 07:50 AM

In addition to Thierry's answer, for data to appear in the Home page, the meters must be added to the Energy Hierarchy in setup. Upon pairing with the Panel Server they are automatically added to the Asset hierarchy, but the user must manually add them to the energy hierarchy. 

Dave_Trenaman_0-1727362162223.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

jorgevasallo
Crewman jorgevasallo
Crewman

Posted: ‎2024-11-29 03:09 PM

0 Likes
0
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-29 03:09 PM

Hola  @vihanger  ,

Has probado actualizar el Firmware del Pas800 a la ultima versión 2.0.0 ???

 

Nos comentas como te fue.

 

Jorge Vasallo 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore