Posted: 2024-02-29 12:27 PM
EEH Allocated Demand Value Calculation
Hello Community, How the Tenant Billing report calculates the Allocated Demand Value from the PDF?
On this example, EEH Records the Max Demand Value of the day 94.5 kW but the Allocated Demand Value in the PDF is 100.7 kW. I would like to confirm if its the Max Average kW on EEH and The max value point from that interval in the PDF. Thank you!
- Labels:
-
Knowledge Base
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-04 01:00 AM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-01 09:28 AM
Hi Emendoz7 the EH online help docs have some information on the algorithm used to calculate the demand charge for Tenant Billing.
https://ecostruxure-energy-one.se.app/relay/cdn/help/en-us/Content/F-Features/TenantBilling.htm#Tari...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-01 01:46 PM
Where is the 100.7 kW value from? if EEH shows Max 94.5 kW for that day. Thank you.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-04 01:00 AM
Please view the calculation details to understand the values in the bill.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-04 05:22 AM
I see how the value is calculated. Thank you.