Dual Circuit Meter Compatibility

EcoStruxure Energy Hub

This forum is dedicated to supporting EcoStruxure Energy Hub service providers and partners with system implementation, reporting skills growth, and in demonstrating profitable improvements in monitored sites. Ask questions, get expert answers and the latest offer news, provide feedback and share community experience and knowledge!

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • EcoStruxure Energy Hub
  • Dual Circuit Meter Compatibility
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thierry_Baudard
Commander Thierry_Baudard Commander
8
Mathew_Losey
Lt. Commander Mathew_Losey Lt. Commander
5
EduardoFainblum
Commander EduardoFainblum Commander
5
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Energy Hub

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Energy Hub
Start a Topic
Solved
DeanZouganelis
Ensign DeanZouganelis Ensign
Ensign

Posted: ‎2023-07-06 01:20 AM

0 Likes
8
1877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-06 01:20 AM

Dual Circuit Meter Compatibility

Hi team,

 

I've had a few people ask about whether dual circuit meters (Modbus) are compatible with EEH. The meter in question is the METSEEMD461R. Has this meter been tested with EEH? 

If it is compatible - How will the data be viewed in the dashboards?

Will we need to provision for 1 or 2 device credits when pricing?

 

Thank you!

Dean 

Labels
  • Labels:
  • Knowledge Base
  • Subscription Modules
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DeanZouganelis
Ensign DeanZouganelis Ensign
Ensign

Posted: ‎2025-10-15 09:55 PM

2 Likes
4
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 09:55 PM

Hi @WestwoodsAutomation ,

 

Good news is multi-channel meters are now supported on Panel Server (FW V2.3 or later) and Energy Hub!

You will need to create a custom model for each channel and upload both to the Panel Server. Both models should share the same voltage registers and/or any other global registers. All other registers Current, Power, Energy etc. should be different. By creating 2 separate models you can reuse the same short ID.

 

I've added a video below of how to add in the models, I used the METSEEMD461R meter. When you add them in, you need to use the same physical ID which is only possible from FW V2.3. If you are using this for Energy Hub, a dual meter will consume 1 device credit.

 

If you need any advice, feel free to message me 🙂

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-07-10 09:49 AM

1 Like
0
1844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-10 09:49 AM

Hi @DeanZouganelis 

 

The list of meter supported by EEH is available on the EEH on line help EEH supported meter list 

and the meter METSEEMD461R  is not in the list so not tested/validated by EEH.

 

During the summer, EEH will support Third party energy meter through Panel Server using Custom models so it will offer the possibility to connect not natively supported meter.

However, My understanding is that it won't be possible to create templates for dual or multi counter like this ref with multiple times the same measurement based on the same PDM short name ID...  So I'm afraid it won't be possible to embed this dual meter.

 

Best regards

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply

Link copied. Please paste this link to share this article on your social media post.

Mathew_Losey
Lt. Commander Mathew_Losey Lt. Commander
Lt. Commander

Posted: ‎2023-07-14 03:16 PM

1 Like
1
1810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-14 03:16 PM

Hi Dean - adding onto Thierry's email below, there is some investigation starting on dual/multi-circuit support in the Panel Server.  

 

We have not specifically validated that particular device, but we can discuss to better understand how the device is used and whether it could be supported with a custom model in Panel Server.

Mathew Losey
EcoStruxure Energy Hub Global Offer Manager
Reply

Link copied. Please paste this link to share this article on your social media post.

WestwoodsAutomation
Crewman WestwoodsAutomation
Crewman

Posted: ‎2025-10-15 05:51 PM

In response to Mathew_Losey
0 Likes
0
672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 05:51 PM

Hi guys

Has there been any updates on this. 

We have some dual meters to interface, howver when setting up the custom modbus profile it appears we are still stuck as we cannot allocate the same short ID.

Reply

Link copied. Please paste this link to share this article on your social media post.

DeanZouganelis
Ensign DeanZouganelis Ensign
Ensign

Posted: ‎2025-10-15 09:55 PM

2 Likes
4
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 09:55 PM

Hi @WestwoodsAutomation ,

 

Good news is multi-channel meters are now supported on Panel Server (FW V2.3 or later) and Energy Hub!

You will need to create a custom model for each channel and upload both to the Panel Server. Both models should share the same voltage registers and/or any other global registers. All other registers Current, Power, Energy etc. should be different. By creating 2 separate models you can reuse the same short ID.

 

I've added a video below of how to add in the models, I used the METSEEMD461R meter. When you add them in, you need to use the same physical ID which is only possible from FW V2.3. If you are using this for Energy Hub, a dual meter will consume 1 device credit.

 

If you need any advice, feel free to message me 🙂

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BrettWabbis
Ensign BrettWabbis
Ensign

Posted: ‎2025-10-16 12:59 AM

In response to DeanZouganelis
0 Likes
3
654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-16 12:59 AM

Thanks so much dean 

I note in your video, that the custom Modbus profile you uploaded included the two profiles in the one upload. 
Is this as simple as creating both modbus profiles in EPC, adding them in the same folder and compressing it, and then adding it to the panel server? (As i believe you can only add one custom model at a time?)

Reply

Link copied. Please paste this link to share this article on your social media post.

BrettWabbis
Ensign BrettWabbis
Ensign

Posted: ‎2025-10-20 06:03 PM

In response to BrettWabbis
0 Likes
0
550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-20 06:03 PM

@DeanZouganelis  

 

Reply

Link copied. Please paste this link to share this article on your social media post.

DeanZouganelis
Ensign DeanZouganelis Ensign
Ensign

Posted: ‎2025-10-20 10:04 PM

In response to BrettWabbis
0 Likes
1
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-20 10:04 PM

Hi @BrettWabbis,

 

Once you have created both Modbus profiles in EPC you can export them at the same time.

First select "Add to Export" and both profiles should appear in your export cart. The compressed folder that downloads will have both Modbus profiles in it. 

DeanZouganelis_1-1761022999914.png

 

DeanZouganelis_0-1761022900990.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BrettWabbis
Ensign BrettWabbis
Ensign

Posted: ‎2025-10-21 09:44 PM

In response to DeanZouganelis
1 Like
0
526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-21 09:44 PM

Thanks so much Dean. I've now completed this! Tahnkyou

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore