In EBO 2024 (6.0), when install or upgrade the Advanced Minimum Polling Interval will be changed from default (0) to the following. However, for sites that have not upgraded or are using Multi-version systems, there should be recommendations to change if less than the new default values. If the values remain at the previous default of 0, the EBO Servers will attempt to poll at the default 500ms, which can overwhelm the communications trunk.