Windows updates and Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Windows updates and Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5410 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Windows updates and Continuum

Picard Product_Support
‎2018-09-07 06:19 AM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:41 AM

Issue

Should automatic updates be turned on for Continuum workstation? Are there certain known issues of updates that have caused problems with Continuum or Webclient?

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • Continuum webClient Server
  • Windows 10
  • Windows XP 
  • Windows Vista
  • Windows Server 2003
  • Windows Server 2008

Cause

Microsoft Windows has an automatic update feature and frequently releases updates which can potentially affect Cyberstation and Webclient Server.

Resolution

  1. Automatic updates should not be turned on for a Continuum or Webclient workstation. The Continuum compatibility matrix indicates Windows Operating Systems, Windows Service packs, SQL Server, .Net and Internet Explorer versions that were tested by Quality Assurance at the time of product release.

    Continuum Quality Assurance does not perform regression testing where new Microsoft updates are tested with Continuum products released in the past.

    Product Support recommends setting Windows updates to one of the other two options to allow for testing of Microsoft updates: Additional details can be found at: http://support.microsoft.com/kb/306525
    1. Download updates for me, but let me choose when to install them
    2. Notify me but don't automatically download or install them
       
  2. There are several specific updates that have caused issues with Cyberstation or Webclient. This is not a comprehensive list. Occasionally updates will break certain features and we discover this from our internal testing or from reports from partners or branches. Here is a list of some updates that have caused issues.
    1. KB835732-  Pinpoint 1.52 crashes when installed on a machine and you are accessing graphics from a network share. If you remove the hotfix the problem goes away.  This is the same hotfix that caused the SmartHeap out of Memory errors that was fixed with SP5 for 1.6. 
    2. KB828741- IIS (Webclient) machines without this patch may receive “Unable to establish a link to the remote Infinity services”
    3. Webclient 1.73 - Any patches that will install .Net Framework 2.0 will cause problems with webclient 1.73 since we don’t start using .Net 2.0 until webclient 1.74.
    4. KB911280 - this update blocks the acc.scp script from setting controller to PPP mode. This will a cause a Cyberstation using RAS controllers to not allow a connection. It will authenticate, but not connect.
    5. KB928366 – Webclient machines that use .Net 1.1(Listed on the compatibility matrix) will receive the error
      "Could not connect to server cause; type missing for member of type object _context id'. Could not create acwppserverproxy."  when opening web pinpoint graphics.  Remove this hotfix or upgrade to webclient 1.74 or greater.
    6. KB929969 – this hotfix does not require a reboot by Microsoft, but can cause the Cyberstation install to fail, if the install is performed before rebooting after the installation of the hotfix. See the Technical bulletin.
    7. KB968749 - SQL Express install fails on XML6 SP2
      See SQL Express install fails on MSXML 6.
Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • 4618
  • patch-deployment
  • PaulFrost22
  • security
  • tuesday
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore