WebStation Graphics Not Working After Java Update & Transition to HTML5

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WebStation Graphics Not Working After Java Update & Transition to HTML5
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2612 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WebStation Graphics Not Working After Java Update & Transition to HTML5

Picard Product_Support
‎2018-09-11 09:44 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-19 06:16 PM

Issue

  • After updating Java (e.g., to Java 7 Update 65 or later), WebStation graphics may appear blank or white. 

    Note: If the error you see is “Error. Click for details” and not a blank window, please refer to the article: WebStation graphics not working after Java updated to Java 7 Update 51.

  • Customers also need clarity on when Java was removed from WebStation and replaced by HTML5.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • Java
  • Building Operation WebStation

Cause

  • Compatibility issues between Java and WebStation in TAC Vista or older Building Operation versions.
  • Java applets were historically used for TGML graphics, causing security warnings and browser compatibility problems.
  • Transition to HTML5 technology eliminated these issues.

Resolution

For Java-related issues (TAC Vista or SBO 1.5 and earlier)

  1. Update Java

    • Install the latest Java version (e.g., 1.7u67).
    • On x64 systems, install both x86 and x64 Java versions.
  2. If issue persists, perform clean reinstall:

    • Close all browsers.
    • Uninstall all Java versions.
    • Backup exception.sites file:
      C:\Users\<username>\AppData\LocalLow\Sun\Java\Deployment\security\exception.sites
      
    • Delete folder:
      C:\Users\<username>\AppData\LocalLow\Sun
      
    • Reinstall latest Java (both x86 and x64 if applicable).
    • Verify Java installation using Java uninstall applet.
    • Restore exception.sites file to its original location.

Technology Transition Note

  • Pre-2014 (SBO 1.0–1.5)

    • TGML graphics displayed using Java applets.
  • 2014–2015 (SBO 1.6)

    • HTML5 Viewer introduced as Beta in WebStation.
    • Users could enable HTML5 manually; Java remained default.
  • 2015–2016 (SBO 1.7)

    • HTML5 fully implemented as the default graphics viewer.
    • Java completely removed from WebStation.
  • 2017 onward (EBO 2.x and beyond)

    • Modern HTML5 UI with responsive design.
    • No plugins required; optimized for Chrome, Edge, Firefox.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (5)
  • Find more articles tagged with:
  • 1.7u65
  • 16511
  • CraigEllis25
  • dialog
  • prompt
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore