Vista Remote workstation cannot get license in Windows 7 with firewall on

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Vista Remote workstation cannot get license in Windows 7 with firewall on
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1545 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Vista Remote workstation cannot get license in Windows 7 with firewall on

Picard Product_Support
‎2018-09-10 05:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:20 PM

Issue

The Vista Remote workstation cannot request the license fro the vista server with the firewall on. If all the ports are opened the license works fine.

Product Line

TAC Vista

Environment

  • Windows 7 32-bit
  • Vista 5.1.6

Cause

Even though ports 135 and 27000 to 27009 are open  Vista license will not work.

The Vendor Daemon (TACLIC.exe) port is by default not specified, and is chosen by the operating system at run time. However, it is possible to specify the TCP/IP port number the daemon use in the license file.

Windows 7 on some installations does not assign a port for TACLIC.exe causing this error.

Resolution

The solution is to manually setup ports for the operation of the license system.

This can be done by editing the Vista License file.

Open the lic file in a text editor

Here is a sample of a standard license header lines.

Please Do not delete this comment line.
SERVER this_host TAC_HL_ID=608806830
VENDOR taclic
USE_SERVER

Here are the changes to fix ports for the license system:

#Please Do not delete this comment line.
SERVER this_host TAC_HL_ID=608806830 27000
VENDOR taclic port=1700
USE_SERVER

This will setup up the LMGRD to use port 27000 and TACLIC.exe will use port 1700.

See Setting the firewall port 135 for a Vista Server running on Windows 7 for information on how to open ports in Windows 7. You will need to select the ports you have defined in your lic file.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6645
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore