Using BACnet Service Tool / RoamIO2 in Windows 10

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using BACnet Service Tool / RoamIO2 in Windows 10
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • CraigEl
    CraigEl
  • StephenYang
    StephenYang
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2589 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using BACnet Service Tool / RoamIO2 in Windows 10

Picard Product_Support
‎2018-09-10 09:43 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 05:34 PM

Issue

Installed the tool under Windows 10 but was unable to assign a port in the tool's connection settings because there are no ports showing in Windows Device Manager.

Product Line

Andover Continuum

Environment

  • RoamIO2
  • BACnet Service Tool

Cause

Windows legacy hardware configuration.

Windows 10 by default does not include the legacy ports.

Resolution

Legacy ports must be added to the Device Manager.

1. Open Device Manager from Windows Control Panel.

2. Select 'Action' then 'Add legacy hardware' or Go to "Start" and type hdwwiz.exe then press Enter

1.PNG

3. Next

2.PNG

4. Next

3.PNG

5. Next

4.PNG

6. Select 'Ports (COM & LTP) then Next

5.PNG

7. Select Microsoft/Standard Serial over Bluetooth link then NEXT

WIndows10Ports.PNG

8. Complete the legacy hardware installation, Device Manager will then show the ports.

ToolSettings.PNG

9. In the Service Tool select the appropriate port.

 

When the connection has been established from Windows PC to RoamIO2 device, the BlueTooth settings in Windows will indicate 'Connected'  NOTE that if it only indicates paired there will be no data transfer even though the blue LED is illuminated on the RoamIO2 device.

(see screenshot below)

RoamIOConnectedBlueTooth.png

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 19609
  • RandyDavis22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore