Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unit Conversion Exceptions feature

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unit Conversion Exceptions feature
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3306 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unit Conversion Exceptions feature

Product_Support
‎2018-09-10 11:26 PM

Last Updated: CraigEl Champion ‎2022-08-08 11:43 PM

Issue

  • Unit Conversion Exceptions
  • Unit selection of 'bar' defaults to N/m2 unit
  • Units are not displaying unit as selected in the properties

Product Line

EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation 1.2 and above

Cause

Building Operation supports both the SI metric system and the US Customary System for units of measurement. The operating system regional settings on which WorkStation is installed determine whether SI units or US Imperial units are displayed. The conversion between the two measurement systems is managed automatically.
For example, the temperature 42,82 °C is stored in Building Operation. A WorkStation on an operating system with the US Customary System converts the temperature and displays it as 109.08 °F.
To display the original unit of a value in WorkStation, open the Properties pane for the value and go to the Unit selection dialog box.

As part of this process some units selected, default to a default display unit, and not what was originally selected.  For example, selecting the pressure unit 'bar' when configured in a SI regional setting will display by default the unit 'N/m2' and not 'bar' as selected.  This functionality is as per design but can be altered by using the Unit Conversion Exceptions feature.

Resolution

First reference Adding a Unit Conversion Exception on the Building Management WebHelp site.  

 In the release version 1.2 and above there is a feature that allows the operator to create unit exceptions, called Unit Conversion Exceptions.  This is located under the Domain folder and allows various conversions for different domains.  The steps below indicate how this is achieved.

  1. Locate the Unit Conversion Exceptions under the required Domain
  2. The Unit Conversion exceptions are now displayed in the Workspace.  The Add remove buttons are located at the bottom of this workspace
  3. Add the Configured unit, which is the selected unit for the variable you wish to be converted
  4. Then change the SI Display Unit and / or US Display Unit to the desired unit you wish the configured unit to be displayed / converted too
  5. Save these changes and confirm that it is now displayed in the desired unit.  In some cases you may need to log out and then back in for the changes to be applied.

Online Web Help is also available here:

If your system is based in US region then you can default you measurement system to US as per Metric vs. English (Imperial) Operating System.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 1.3
  • 1.4
  • 1.5
  • 11962
  • HernanUruena24
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore