Unable to open BACnet Device/objects. "Object_Identifier" error.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to open BACnet Device/objects. "Object_Identifier" error.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3522 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to open BACnet Device/objects. "Object_Identifier" error.

Picard Product_Support
‎2018-09-07 08:49 AM

Last Updated: Sisko GavinHe Sisko ‎2023-05-23 03:23 AM

Issue

Seeing "An Object_Identifier has been specified for an object that does not exist in the object database of the addressed BACnet device", when trying to open a BACnet Device in Continuum

Product Line

Andover Continuum

Environment

  • bCX 4040
  • BACnet

Cause

When trying to send a controller's obejcts to the Database on the BACnet side the following messages are seen in the Distribution Properties window.


10/10/2013 12:50:07 PM The operation 'Save to Database' is finished.
10/10/2013 12:50:07 PM Unable to save objects to the database from Id:36922175.
          An Object_Identifier has been specified for an object that does not exist in the object database of the addressed BACnet device.
10/10/2013 12:50:07 PM The operation 'Save to Database' is starting.

 

In the case of the affected controller being a bCX, all b3's underneath the bCX are able to be seen and their objects opened, but a user is unable to open any of the objects in the bCX itself on the BACnet side of the Continuum system tree.  Some/all objects are either not located in the BACnet side of the bCX Device or they have been malformed as they were initially created.

Resolution

The Device needs to be removed and re-discovered

  1. Delete the BACnet side of the bCX Device.
  2. Perform a "Find new BACnet Devices" from the Root.
  3. Then "Send to Database" on the BACnet side to upload all of the BACnet objects back into the Database.
     
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 14666
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore