Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Unable to enable or disable Enhanced Alarm Logging or Alarm Delivery flags in Database Initialization

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to enable or disable Enhanced Alarm Logging or Alarm Delivery flags in Database Initialization
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1883 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to enable or disable Enhanced Alarm Logging or Alarm Delivery flags in Database Initialization

Picard Product_Support
‎2018-09-11 06:26 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:36 AM

Issue

Unable to enable or disable Enhanced Alarm Logging or Enhanced Alarm Delivery flags in Database Initialization. The Enhanced Alarm Logging flag goes back to what it was set to before making the change and the Enhanced Alarm Delivery flag is greyed out and uneditable.

Product Line

Andover Continuum

Environment

Continuum Database Initialization

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

The owner of the ContinuumDB is set to something other than the default andover97.

In this specific case it was set to SA. The SA user was unable to write these changes to the database hence why the settings kept reverting back. To compound the issue it was found that an andover97 user had been created under the Security folder in the ContinuumDB, this then blocked attempts to change the owner to the correct andover97 user.

Resolution

  1. Backup the ContinuumDB before making any changes. See Move / Backup / Restore a database on a Single User SQL2005 Express system.
  2. Attempt to change the db owner with the below query using the sp_changedbowner stored procedure. Select "New Query" and copy the query text shown below. Run the query.
    USE [ContinuumDB]
    GO
    sp_changedbowner 'andover97'
    GO
  3. If this produces an error "The proposed new database owner is already a user or aliased in the database" then see Unable to change the ContinuumDB database owner using the stored procedure sp_changedbowner for instructions on how to drop the incorrect user so we can use the correct one.
  4. After successfully dropping the user from the ContinuumDB, re-run the query in step 2 above to change the database owner to andover97.  
  5. After successfully setting andover97 to the database owner you should now be able to toggle the Enhanced Alarm Logging and Enhanced Alarm Delivery options in Database Initialization. If you want these enabled; toggle them both off, update the database, toggle them both on, update the database again. This will ensure they have been enabled properly.

Note: The definitive check to see if the Enhanced Alarm logging and Enhanced alarm delivery are both enabled is by checking the dbo.ACCDBVersion table in the SQL database using SQL Server Management Studio (or Express).

New Alarm Logging and New Alarm Delivery should both be set to 1.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 13811
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore