Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Unable to discover BACnet devices after changing IP Address on AS or ES

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to discover BACnet devices after changing IP Address on AS or ES
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7162 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to discover BACnet devices after changing IP Address on AS or ES

Picard Product_Support
‎2018-09-10 11:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:53 PM

Issue

Unable to discover BACnet devices from a BACnet interface, discover broadcast address and/or devices are offline after changing IP Address on AS or ES. Bacnet devices are offline after a power cycle or loss of IP connection at the AS or ES.

Product Line

EcoStruxure Building Operation

Environment

StruxureWare Building Operations site using devices configured with BACnet

Cause

Broadcasting on wrong network from either the Automation Server or the Enterprise Server can be a problem. In the example below an AS is broadcasting for a BACnet device (in this case a MNB Controller). In the IP Network for the BACnet Interface, check your settings for Broadcast Address. The key is to ensure your BACnet broadcast address is in the correct range.

 

In this first screen capture, we have a BACnet network interface using the IP Network with a red failure to communicate indicator on the MNB.

In this example, the broadcast is on 192.168.1.255

Resolution

The computer being used as well as the BACnet devices we want to discover and use are in the following IP network and settings:

Changing the broadcast address to match what the BACnet network is using resolves the issue (BBMD and BBDT from Enterprise Server or Automation Server).

Lastly, choose to discover devices

For subnet calculations and how to setup your subnet addresses, several recommended calculator are SuperNet Online or SubnetMask a downloadable program from Solar Winds. 


When the IP Network broadcast address is set incorrectly, a Wireshark capture may reveal that no WHO-IS message is sent out from the SmartStruxure server when a device discovery is attempted.

When in doubt as to whether the 'IP Broadcast Address' is correct, a simple test is to set the IP Broadcast address to 255.255.255.255, doing so will instruct the SmartStruxure server to broadcast on ALL subnets, if the problem was caused by an incorrect broadcast address it will be resolved but care must be taken not to leave the default address set to 255.255.255.255 as this will cause unnecessary traffic on all sub-nets, instead, review your calculations for what the appropriate broadcast address should be and set it appropriately.


Key Concept: The AS will retain the Broadcast address, and if moved to a new Subnet, the old Broadcast address must be updated. One can do either of the following: 

  1. Edit the IP Broadcast Address Setting 
  2. Delete the BACnet Interface and recreate in the new Subnet
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 8272
Was this article helpful? Yes No
34% helpful (1/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore