Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Unable to connect to a BCX or 9680 configuration page

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to connect to a BCX or 9680 configuration page
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4520 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to connect to a BCX or 9680 configuration page

Picard Product_Support
‎2018-09-06 02:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-18 11:05 PM

Issue

Unable to connect to a BCX configuration page

Product Line

Andover Continuum

Environment

Continuum BCX9640 and 4040

Cause

404 Page not found error accessing the configuration page using the controller IP in a browser

Resolution

Note: This document is for troubleshooting help, it is not a comprehensive BCX setup guide. Please refer to the BCX1 Technical Reference for detailed setup instructions.

 

  1. Using a LAN or a cross-over cable?

    If the BCX is on a LAN and was working before, remove the LAN cable from the BCX and try to ping the BCX. If you get a response then you have a duplicate IP.

  2. Same subnet?

    Make sure DHCP is disabled on your computer.

  3. Use a straight-through or cross-over cable to access the BCX directly.

    Has this cable been used successfully before?

  4. Reset the BCX to the default IP.

    The button is under the cover, top right. Be sure to hold down the IP reset button for about 20 seconds

  5. Is the controller in bootloader mode?

    This can be seen by observing the CPU light flashing rapidly, approximately two times a second (2 Hz at 50% duty). Flashing the application through Cyberstation may fix this and enable you to get back into the controller. Even though access to the config page is not available, the update OS button in Continuum using the controller's Network setting and ACCNet ID may be accessible to perform a firmware upgrade.

  6. Ping the IP from a DOS prompt, can the BCX be pinged?

    Ex. Ping 169.254.1.1

  7. Use Ipconfig /all to see your PCs network settings.

    The best case scenario is to be on the same subnet or connect directly.

  8. Are there multiple NIC cards on the PC? (Ex. Ethernet and wireless on a laptop)

    Disable the wireless adapter or other adapters. Continuum does not support a multiple NIC card configuration.

  9. Run Wireshark to get a capture between the BCX and The PC.

    Remove power from the BCX and reapply power. When the BCX starts it sends a gratuitous ARP that will indicate the IP address within the BCX. It may be a different IP than expected.

  10. Did the issue of not accessing the web page happen after a power outage?

    Is the CPU light flashing amber and it was flashing green before and no one has flashed the controller? Is the CPU light solid amber? If so, contact support for assistance.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 2800
  • AlanWood22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore