Troubleshooting for bringing a Reader Expander online.
Building Automation Knowledge Base
Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Module addressing has not been configured or is incorrect.
Resolution
Check the following:
1. Controller (SP_C) Module addressing is correct.
When creating the controller for the first time you will need to register it as a Reader Expander to be able to use it's reader ports. Go to the Configuration tab of the controller and set "Register as Reader Expander" to 1 and the Lock Outputs to the default "Controller PGM 3/4 outputs" setting.
2. Reader Expander Module address.
A new module from the factory will default to an id of 254, this will need to be changed. If you only have the controller and one expander module then the SP-C will be id=1 so make the second expander id=2.
3. Health status.
Check the Health status of your controller to see if anything shows up there.
4. Update.
Update your modules to download changes, review the health status again.