Thermistor type selection in EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Thermistor type selection in EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
6 Likes
10131 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Thermistor type selection in EBO

Administrator CraigEl Administrator
‎2021-09-16 11:34 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:50 AM

Issue

Confusion over the thermistor type selection for an EBO Temperature Input object

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation I/O Module
  • Building Operation Automation Server Bundled
  • Building Operation Multi-purpose Controller (MPC)
  • Building Operation Room Controller (RPC)
  • Building Operation IP-IO

Cause

The Thermistor type selection lists sensor "Types" I through V

 

thermistortypes.png

 

This is confusing since, for example, the Continuum sensor is listed as 10k Type I but in manufacturers literature and temperature vs resistance tables is often referred to as 10k Type 3

Resolution

The reference to Thermistor 10k Type in the selection list is an internal reference and not intended to refer to the types listed in manufacturers literature and temperature vs resistance tables. For reference the selections refer to the following sensor types:

 

  • Thermistor 10k Type I (Continuum) – Thermistor 10K4A1 also referred to as 10K Type 3 - SpaceLogic Sensors (as SLASXXX, SLAWXXX and SLABXXX), STx5xx Sensors (see HVAC Sensor catalog for details)
  • Thermistor 10k Type II (I/NET) – Thermistor 10K2A1 Dale/Vishay - STx20x Sensors (see HVAC Sensor catalog for details)
  • Thermistor 10k Type III (Satchwell) – Thermistor 10K3A1 (No Longer Applicable for Satchwell sensors)
  • Thermistor 10k Linearized (Satchwell DxT - Type T) - STx6xx Sensors (see HVAC Sensor catalog for details)
  • Thermistor 10k Type IV (FD) – Thermistor 10K4A1 type ‘G’ (U.S. Sensor)
  • Thermistor 10k Type V (FD w/ 11k shunt ) – Thermistor 10K type ‘G’ (U.S. Sensor) with external 11k ohm shunt resistor installed
  • Thermistor 1.8k (Xenta) – Thermistor type 1.8KA1 - STx1xx Sensors (see HVAC Sensor catalog for details)
  • Thermistor 1k (Balco) – (not a thermistor) RTD, 1000 ohm Balco
  • Thermistor 20k (Honeywell) – Thermistor 20K6A1 type H
  • Thermistor 2.2k (Johnson Controls) – 2.2K3A1

 

Refer to the Temperature Sensor Resistance Charts Knowledge Base article for temperature vs resistance charts for these sensor types and others.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • CraigEllis21
  • DavidShore22
  • GaryMontague23
  • MahmoudSayed23
  • TreyBoothe25
Was this article helpful? Yes No
100% helpful (10/10)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore