Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

The Lua AND function returns unexpected results

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The Lua AND function returns unexpected results
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MaximeLaudren
    MaximeLaudren
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1725 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The Lua AND function returns unexpected results

Picard Product_Support
‎2018-09-11 02:42 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-18 11:24 PM

Issue

There are two variables:
INDIT =0
koll1_p=1

- When using AND:

DEV700.BO1=(INDIT and koll1_p) --prim sziv1

The result is DEV700.BO1=1

- When using *:

DEV700.BO1=(INDIT * koll1_p) --prim sziv1

The result is correct DEV700.BO1=0

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager (MPM)

Cause

The simple issue here is that the and keyword is a logical operator, however the variables being compared are numeric.

Contrary to many other languages, a Lua variable is not typed, which means that the kind of value it stores are not constrained and can actually change during a program execution:

Boolean Designates a variable which can hold the true or false values. It is important to note that true or false are not numbers and do not equal 1 or 0.

That is why the mathematical multiplier * keyword works in this instance but the logical and does not.

Resolution

The logical operators are and, or, and not. Like control structures, all logical operators consider false and nil as false and anything else as true. The operator and returns its first argument if it is false; otherwise, it returns its second argument. The operator or returns its first argument if it is not false; otherwise, it returns its second argument:

print(4 and 5)         --> 5
    print(nil and 13)      --> nil
    print(false and 13)    --> false
    print(4 or 5)          --> 4
    print(false or 5)      --> 5

Both and and or use short-cut evaluation, that is, they evaluate their second operand only when necessary.

Essentially to use the and operator with numeric values they will first need to be evaluated into true or false states. For example:

If INDIT ~=0 then x= true else x= false end
If koll1_p ~=0 then y= true else y= false end

DEV700.BO1=(x and y)

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (2)
  • Find more articles tagged with:
  • 16318
  • MaximeLaudren22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore