Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed on the same machine

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed on the same machine
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2822 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed on the same machine

Picard Product_Support
‎2018-09-07 11:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:09 PM

Issue

When TAC Vista and the SmartStruxure Enterprise server are installed on the same machine the EcoStruxure web service object will not connect to the Vista Server.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • TAC Vista
  • SmartStruxure Solution
  • EcoStruxure Web Services
  • TAC Vista SmartStruxure Interface 1.0

Cause

The default ports used by the SmartStruxure Enterprise server are HTTP 80 and HTTPS 443. These are the exact same ports used for the communication between the TAC Vista SmartStruxure Interface and EcoStruxure Web Services

Resolution

TAC Vista SmartStruxure Interface settings change the HTTP and HTTPS ports to something that is available and not in use on the machine. In the example below HTTP 8181 and HTTPS 8191 are used. After these ports are changed click apply and stop and restart the TAC Vista SmartStruxure Interface service.

After these port changes are made login to the Enterprise server and select properties on the TAC Vista web services object. Change the service URL to the localhost address and the proper port that was chosen in the TAC Vista SmartStruxure Interface settings. In the example below http://localhost:8181/EcoStruxure/DataExchange was used. The local IP address could also be used in place of the localhost if needed.

Another point needs to be kept in mind is that only the user in the default System user group can be used. Don't try to create other System group. And all the letters in the password need to be in capital in the password field of the window above. This is a defect that will be addressed in the next release of TAC Vista to SmartStruxure interface.

For how to create Vista interface in SmartStruxure, refer to How to Create TAC Vista Interface to SmartStruxure.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 14374
  • offline
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore