How to Create TAC Vista Interface to SmartStruxure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Create TAC Vista Interface to SmartStruxure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
4638 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Create TAC Vista Interface to SmartStruxure

Picard Product_Support
‎2018-09-11 05:52 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Issue

How to transfer data from TAC Vista to EBO(EcoStruxure Building Operation)

as a temporarily solution while a transition between TAC Vista and EBO is done? 

 

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • TAC Vista
  • SmartStruxure Solution
  • EcoStruxure Web Services
  • TAC Vista SmartStruxure Interface 1.5

Cause

If EBO need data from TAC Vista during a transition period the TAC Vista SmartStruxure interface can be used.

 

Resolution

Please see the video or follow the instructions below:

 

  1. On the Vista server(s) install the TAC Vista SmartStruxure Interface first. Refer to TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed... if there are any issues installing or getting the two programs to communicate when on the same PC.
  2. In StruxureWare Workstation, on the Enterprise server object or the Automation server object right click and create new interface, and select the EcoStruxure Web Service interface in Workstation. Click next.

  3. In the Server, enter the IP address of Vista server. If it is local, just use localhost. Enter the username and password of Vista Server. Pay attention that only the user in the default System user group can be used. Don't try to create other System group. And all the letters in the password field need to be in capital letters. This is a defect that will be addressed in the next release of TAC Vista to SmartStruxure interface. Please be selective with the port that you are using. If the Vista to SmartStruxure Interface program is on the same PC as the Enterprise server than a different port other than 80 or 443 will have to be used. Please refer to TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed... if the two softwares need to be on the same machine. Click Create.

  4. The next step is to Host TAC Vista objects into SmartStruxure. Refer to How to host TAC Vista objects using Web Services in StruxureWare Building Operation for the guide of how to host Vista objects into SmartStruxure.

NOTE:

There is a defect for Version 1.0 of TAC Vista to SmartStruxure interface under Non-English operation system. The EcoStruxure Web Services interface will not come online in SmartStruxure. Refer to TAC Vista to SmartStruxure Interface does not connect in non-English Operation System for solution.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 15162
  • JonasBrissman22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore