Standard Output Window displays the following error: Java.net.socketexception.reset
  • Standard Output Window displays the following error: Java.net.socketexception.reset
  • Cody_Failinger
    Cody_Failinger
  • Julio_Cortes
    Julio_Cortes
  • CraigEl
    CraigEl
‎2018-09-06 12:57 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:35 PM
TAC IA Series
R2 Niagara
The IP network has two NIC cards assigned the same address.  This results in a  Duplicate IP
Use WireShark to Find the duplicate IP and re-assign a new ip to the server or UNC IP. For more detail see Using WireShark to analyse communications on an Ethernet network.