Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

Sigma controller regularly warmstarts or resets

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma controller regularly warmstarts or resets
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1504 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma controller regularly warmstarts or resets

Picard Product_Support
‎2018-09-10 01:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:40 PM

Issue

Controller regularly warmstarts or resets every 5 minutes. The site was upgraded from a BAS system

Product Line

Satchwell Sigma

Environment

  • Sigma
  • Controller 1 warm start
  • BAS
  • Wireshark

Cause

In Sigma each device (server, controller and DNN) must be unique, in BAS this was not the case as terminal and outstations could share the same number.

The resetting controller is receiving requests for files or alarm data that was previously routed to a BAS terminal, the Sigma controller does not handle the data and resets/warmstarts. 

The previous BAS terminal number would have been the same as the controller number, typically T1 and OSN1.  When upgraded to Sigma the BAS terminal number would have been changed to a new designation but some of the system configuration has not been updated correctly.

Resolution

  1. Alarm routing:  Check that all the alarm routing in the object files (R1, R2, R3, and R4) are set correctly.  Some systems use single destinations such as T1, if this is found and the destination number matches a controller number then this must be changed. (See Node reset messages are received at regular time intervals after a BAS 2800+ to Sigma upgrade)
    To search for possible incorrect routing destinations use the latest Sigview utility and search for any alarm routing that matches a controller number.
    Note: Typically device number 1 is the issue, but this may not be the case in all situations and another device number may have been duplicated.
  2. Operlist.txt Files: Check that all the operlist.txt files have been modified to the latest version and none contain the older BAS format. For example the wrong entries are;
    1 C:\Bas\Data\OSN2\ROUTESET.REC    ROUTESET.REC
    1 C:\Bas\Data\OSN2\LOOKOSN.REC     LOOKOSN.REC
    1 C:\Bas\Data\OSN2\PNTFLE.REC      PNTFLE.REC
    With Sigma can be;
    ;This is a dummy OPERLIST.TXT
     
    (Note: CRLF (Carriage Return & Line Feed) after the line)
    The dummy operlist.txt file will be created automatically by Sigma if the existing operlist.txt file is deleted from the server and then a download to the controller is performed.
  3. Default/Backup server number: Using the Diagnostics - View Comms Stats, check that all the controllers on the system do not have the default or backup server number configured the same as a controller number.
  4. Logging Servers: Using the Diagnostics - View Logging Servers, check that no logging data sets have been created with a server number matching an existing controller number.
  5. Wireshark Trace: If neither of the above help then it may be possible to look at the Ethernet data packets being received by the controller (obviously will not work if the controller is on an ARCnet LAN).   
    1. Set up a laptop with Wireshark (see Using WireShark to analyse communications on an Ethernet network) with an Ethernet hub at the controller.
    2. Run the trace until a reset/warmstart is observed at the controller
    3. Save the trace and email to Product Support or add and apply the following filter to show only those data packets being sent to the controller:
      ip.dst==192.168.2.1   (Change the IP Address to match that used by the controller)
      Look for packets that appear to come from another controller (source IP address).  For example below shows a request for the Lookosn.rec file on controller 1 (fault with operlist.txt file).

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 5551
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.