Sigma Lon card is applicationless and cannot be reset by IC3 LON controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Lon card is applicationless and cannot be reset by IC3 LON controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • RandyDavis
    RandyDavis
  • Gary
    Gary
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • RyanSuar
    RyanSuar

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2050 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Lon card is applicationless and cannot be reset by IC3 LON controller

Picard Product_Support
‎2018-09-09 10:28 PM

Issue

Cannot commission an IC3 LON controller in LonMaker. It has become applicationless and the red service LED is flashing or is permanently lit. 

Product Line

Satchwell Sigma

Environment

  • Satchwell Sigma Controller
  • IC3 IC LON FTT-10
  • NodeUtil

Cause

The Echelon chip has become 'locked' and requires resetting.  This can be caused by corrupted controller files, very high LON traffic (> 50% Bandwidth), or the controller has started from "start-up mode" or cold start.

 

Resolution

The Echelon chip can be reset using NodeUtil.exe  .  This is a DOS-based program that can be loaded onto a laptop with an FTT-10 Echelon adaptor. A clean working set of controller files will be downloaded to the device.

  1. In the case of a flashing red LED - Download 'clean' files to the controller
  2. Start NodeUtil on the laptop and plug LON cable into the controller
  3. Reset controller (via onboard reset button)
  4. Activate the plug-in LON card service pin and the Neuron Id should appear on the laptop. Note: If further controller resets and service pin activations fail to generate the service pin echo then discard the plug-in card and replace with a new one.
  5. From the NodeUtil menu select 'R' and enter the Node Id number
  6. Confirm the reset of 3150 Node
  7. The service LED should stop flashing and the controller should now be 'Configured' that is not 'applicationless'
  8. In the red LED is permanently lit - Download 'clean' files to the controller, the Echelon chip will become locked again. Repeat the reset procedure using NodeUtil.exe, this will allow the controller to work, but the plug-in card will need to be replaced.

Example of NodeUtil process;

NODEUTIL> (H)elp with commands
A -- (A)dd node to list.
D -- Set the (D)omain of the network interface.
E -- (E)xit this application and return to DOS.
F -- (F)ind nodes in the current domain.
G -- (G)o to node menu.............
H -- (H)elp with commands.
L -- Display node (L)ist.
M -- Change node (M)ode or state.
O -- Redirect (O)utput to a file.
P -- Send a service (P)in message.
R -- (R)eboot 3150 node.
S -- Report node (S)tatus and statistics.
T -- (T)ransceiver parameters.
V -- Control (V)erbose modes.
W -- (W)ink a node.
Z -- Shell out to DOS.
NODEUTIL> Received an ID message from node 2.
Program ID is ICLON1a
NODEUTIL> Received an ID message from node 2.
NODEUTIL> (R)eboot 3150 node
Enter node id for reboot (0-2) [2] :2
*** Neuron 3150: Rebooting will reset comm. params, node state
on-chip EEPROM variables and buffer configuration
Are you sure you really want to do this? (Y/[N]): Successfully rebooted node
NODEUTIL>

A second solution has been provided by a customer and could be considered if the above suggestions does not provide a solution.

Alternative reset procedure provided by a customer is as follows: -

1. Removed the IC LON from both the LON and the Sigma network.
2. I used SCDU tool to re-node the ICLON to a random IP address, which I believe cleared the database and the files etc.
3. I removed the power form the ICLON and then removed the LON daughterboard card from the ICLON mainboard.
4. Re-instated power and re-installed the LON daughterboard card.
5. Connected with NODE Utility as per the product data-sheet below. And cleared the LON comms buffers as the suggested method.
6. Checked that the red constant service light ceased from the constant illumination. And witnessed that the Green LON heartbeat LED was operational.
7. Re-Node the ICLON to the original IP and check operation.

* The Sigma IC-LON plug-in card can be purchased using the part number S-LON. The S-LON has been discontinued as of 29th December 2017 and it is now in the service period (limited quantities available for purchase). Refer to PA-00528 for details.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
NODEUTIL.zip
Osn117.zip
Tags (13)
  • Find more articles tagged with:
  • 5287
  • add
  • exit
  • find
  • GaryMontague19
  • go
  • help
  • output
  • RyanSuar19
  • status
  • transceiver
  • verbose
  • wink
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of