Difficulty in configuring and interpreting 32-bit values when interfacing an IC3-Modbus with a third-party Modbus device.
Satchwell BAS & Sigma
  • Satchwell Sigma
  • IC3 Modbus
  • Devices using 32-bit Modbus registers
Incorrect configuration of the gateway.txt file and unclear device documentation can read to errors in reading 32-bit values.
The following steps outline the troubleshooting and resolution process:
  1. Initial Configuration Attempt
    • The gateway.txt file was configured as per initial guidance.
    • Error encountered: Function code 4 was not allowed.
  2. Function Code Correction
    • Modified gateway.txt to use function code 3, resolving the function code error.
    • New issue: Register address still caused an error.
  3. Address Correction Attempt
    • Updated string to:
      304,3,3,0xC652,1,1,0,0,0
      This eliminated address errors but did not return the correct value.
  4. Data Format Adjustment (Unswapped)
    • Changed string to:
      304,3,3,0xC652,1,0x0202,0,0,0
      This represents a 32-bit unsigned value (not swapped).
      Result: Still incorrect value.
  5. Final Configuration (Swapped)
      304,3,3,0xC652,1,0x1202,0,0,0
      This represents a 32-bit unsigned value (swapped).
      Result: Correct value returned.