Security Expert PSU has Fault Icon lit and Status Light Flashing Red

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Security Expert PSU has Fault Icon lit and Status Light Flashing Red
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2427 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Security Expert PSU has Fault Icon lit and Status Light Flashing Red

Picard Product_Support
‎2018-09-10 07:49 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:58 AM

Issue

Security Expert PSU has Fault Icon lit and Status Light Flashing Red Every 3 Seconds indicating an issue with PSU Addressing

Product Line

EcoStruxure Security Expert

Environment

Security Expert PSU

Cause

The module address 254 is the default value which all modules are shipped with and is outside the range the controller can accept. This must therefore be changed during commissioning. See Page 41 of the Operator Reference Manual for details.

There is an overall limit of 250 modules that can be connected to a single controller with the following limit on each type of module:

  • Keypad Modules: 200
  • Input Expanders: 248
  • Reader Expanders: 64
  • Output Expanders: 32

The module addressing is defined per module type not by the position of that module on the network. You could have all modules at the same address as long as they are all different types.

Example:

With the following modules we could have all modules be set to use address 1:

  • 1 x Controller
  • 1 x Keypad
  • 1 x Reader Expander (In this case onboard Reader)
  • 1 x Analogue Expander (PSU)

Resolution

1. Right Click on the SP-C Controller and select Module Addressing. Change the Address of the Analog Expander (PSU) from its default value of 254 in this case to a value of 1.

PSU Address Real.png

2. Then Update all Modules.

3. Select the Analog Expander (PSU) in the System and also change its Physical Address to also be 1. Save the changes.

PSU Address DB Mod.png

4. The PSU should now come online and the Fault Icon on the PSU will no longer be lit.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • 19823
  • AdamSteele20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore