SP-C Controllers randomly going offline

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SP-C Controllers randomly going offline
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • David_Kendrick
    David_Kendrick
  • AdamSteele
    AdamSteele
  • Chris_Asbury
    Chris_Asbury
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3521 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SP-C Controllers randomly going offline

Admiral David_Kendrick Admiral
‎2019-07-24 11:14 PM

Last Updated: Commander Chris_Asbury Commander ‎2022-08-10 12:52 AM

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Issue

  • SP-C Controllers randomly going offline / online.  Restarting the controller resolves the issue for a short period of time.
  • SP-C Controller ports showing TIME_WAIT when a netstat command is run.

Product Line

EcoStruxure Security Expert

Environment

Security Expert Controller (SP-C)

Cause

Under normal conditions an SP-C needs to update the Security Expert Server with new data. During this time the IP Socket of the SP-C is in a Waiting State, refusing to communicate to anyone else while waiting for an opportunity to upload. Once the controllers data has been uploaded to the server however the controller releases the IP Socket and it is open again to new communication.

In an extremely small number of cases the SP-C controller goes into this waiting state as usual but then never comes out of that state, holding onto the IP Socket forever and blocking any further communication until the controller is power reset.

This only affects a very small percentage of SP-C controllers running Microsoft Windows CE OS Version 16.

Resolution

In these extremely rare cases the first step is to identify if the affected controllers are indeed running OS Version16.  For SP-C Firmware builds before 2.08.921

  1. Log into the controllers configuration web page.
  2. Browse to the Configuration tab.
  3. Check the OS Version field at the bottom of the page.

For SP-C Firmware build 2.08.921 and above the OS is now shown in a different location.

 

Once it is clear, that the OS is version 16, Product Support can be contacted to arrange to upgrade the controller OS to Version 20 (or greater) as is found in SP-C controllers shipping now. As this is a high risk procedure and can result in complete failure of the controller if anything goes wrong there are two options for upgrading the OS.

  1. Install the affected controller on a test bench with remote access for Product Support to remote in to and perform the update.
  2. Have the controller sent back to the factory to be updated and returned to site.

Both options will require replacing the controller with temporary stock while the upgrade is being performed.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (8)
  • Find more articles tagged with:
  • AdamSteele19
  • AdamSteele20
  • AdamSteele22
  • AdamSteele24
  • ChrisAsbury22
  • DavidKendrick19
  • DavidKendrick21
  • IntLink_169606
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of