SE(R)8000 series short and long messages

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SE(R)8000 series short and long messages
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • SaidSawan
    SaidSawan
  • RyanSuar
    RyanSuar
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2647 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SE(R)8000 series short and long messages

Picard Product_Support
‎2018-09-11 01:54 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:57 PM

Issue

SE(R)8000 series short and long messages

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation

Environment

  • SE8000 Series Room Controllers
  • SER8000 Series Room Controllers
  • Ex. Viconics branding VT8000 Series
  • EcoStruxure Building Operation

Cause

Configuration of the SE(R)8000 series short and long messages

Resolution

The short and long messages are set via BACnet. Take note that the short and long messages do not hold when power to the SE8000 is turned off. This is because currently, the messages are stored in RAM. The workaround is to change the name (from the AS) and back again then save to get it to display on the unit again. Below is the procedure to change the short and long messages in EcoStruxure Building Operation.

Short Message:

The Short Message can be written to the SE8000 room controller by populating the "Location" Property with the message

this-is-a-short-message-2.png

 

Long Message:

The Long Message can be written to the SE8000 room controller by populating the "Description" Property with the message

this-is-a-long-message-2.png

The message however will not get displayed until the "Display Long Screen Message" has been activated.

display-long-message-2.png

Optional: you can also choose the color of the long message background by changing the "Long Message Background Color".

long-message-background-color-2.png
 


 

Discrepancy on the text written to the device, and the text shown on the device

In some cases when using non-English characters in the messages, the text on the SE8000 will not be rendered as expected. The issue is caused by SE8300 not conforming to BACnet standard in string encoding and decoding. The workaround is to set "BACnet string encoding" property of the device to "ISO 8859-1(Latin-1)", or other encoding the device supports.

SE8300 claims to support BACnet protocol revision 10, which requires the conforming device to interpret Character Set 0 as UTF-8 string. In 1.9, SBO started to write to devices using Character Set 0 for unicode strings, but the SE8300 fails to decode it.
Setting the "BACnet string encoding" to Latin-1 for the devices fixes the problem. 

fix_string_encoding_small.png

Labels (2)
Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
Tags (6)
  • Find more articles tagged with:
  • 17087
  • mpm
  • se8350
  • smartstruxure
  • webstation
  • workstation
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore