Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Replacing Automation Server hardware

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing Automation Server hardware
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • JohnBoehmer
    JohnBoehmer
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3995 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing Automation Server hardware

Picard Product_Support
‎2018-09-06 10:47 AM

Last Updated: Sisko DavidChild Sisko ‎2020-04-07 02:16 AM

Issue

  • What is the proper way to replace AS hardware for an existing node.
  • Cannot get the AS to come online in the Enterprise Server after replacing the AS hardware for an existing node.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server - Classic (AS)
  • Building Operation Automation Server - Premium (AS-P)
  • Building Operation Automation Server - Bundled (AS-B)

Cause

  • To replace the AS hardware, a backup must have been made from the original AS while it was online. 
  • Simply changing the controller name, IP information, and domain  information in the AS will not be sufficient for bringing the controller online in the ES.

Before the new automation server can be brought online, the backup from the original controller must be restored to the new AS directly.

Resolution

This procedure assumes that a backup of the original AS is available.

  1. From Device Administrator and the USB interface, run the SetIP command to configure the following information in the new AS to match the original AS configuration.
    Note: You will have to use the version of Device Administrator that matches the replacement AS firmware.
  2. If necessary, use the appropriate version of Device Administrator to Upgrade or downgrade the firmware in the new AS so that it matches the Enterprise Server and/or the original AS hardware firmware.
  3. Install the AS then backplane.
  4. From StruxureWare workstation, log into the AS using the hardware's IP address for the Server field.
  5. Right click on the server name and select Restore.
  6. If the backup does not appear in the Available restore points window, click on Import Backup Set and browse to the backup file.
  7. Select Configuration only or All data in the window on the left.
  8. Select restore.
  9. Once the restore has completed the AS displays a solid green status light, log off the AS and log into the ES.

The controller should now appear online in the ES.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 12076
  • DavidChild20
  • installation
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore