Regular increase of LonWorks traffic
  • Regular increase of LonWorks traffic
  • RobertAndriolo
    RobertAndriolo
  • RandyDavis
    RandyDavis
  • MikaelKrantz
    MikaelKrantz
  • PeterLarsen
    PeterLarsen
Guinan MikaelKrantz Guinan
‎2021-11-04 12:06 PM
Last Updated: Administrator CraigEl Administrator ‎2023-02-28 03:48 PM
With the same time interval as the trend log, the traffic on the LonWorks network increases for a short period. This can be seen by a spike in the LPA log when viewing the bandwidth.
  • Building Operation Workstation
  • Lonworks
The LonWorks traffic increases with the same time interval as the trend log.
To ensure we could log values in the trend log from a LonWorks device, a subscription is set up about 30 seconds before the value should be logged. After the value is logged, the subscription is removed until the next log interval. A good solution to flatten a spike caused by this issue is to stagger the times of the LonWorks trend logs. This will ensure the subscription for all the logs do not happen at the same time.