Recovering a JACE using a Niagara 4 Clean Distribution

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Recovering a JACE using a Niagara 4 Clean Distribution
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • WaynePeters
    WaynePeters
  • RandyDavis
    RandyDavis
  • David_Kendrick
    David_Kendrick
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
10312 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Recovering a JACE using a Niagara 4 Clean Distribution

Picard Product_Support
‎2018-09-10 09:50 AM

Last Updated: Administrator CraigEl Administrator ‎2021-12-21 01:14 PM

Issue

The Niagara 4 JACE's platform daemon fails to start making it impossible to login and configure using Workbench tools such as the Commissioning Wizard or Dist File Installer. The error within the serial shell typically indicates ... /proc/boot/ksh: niagarad: cannot execute - No such file or directory.

Product Line

TAC IA Series

Environment

  • Niagara 4
  • JACE-603
  • JACE-645
  • JACE-600E
  • JACE 8000

Cause

This can occur as a result of an Incorrect or failed upgrade or improper downgrade without first installing a clean distribution.

Resolution

Requirements - You will need the following to complete the recovery steps:

  • A terminal emulator such as PuTTY
  • A SFTP client such as FileZilla
  • Serial-Shell cable for your JACE hardware model (specified in the .PDFs below)
  • The Niagara 4 Clean Dist file for your JACE hardware
  • A zip file utility such as 7-Zip
  • The hardware and startup documentation for your JACE model (provided with Niagara 4 installer)

Obtain recovery files from the Niagara 4 Clean Dist File for the matching hardware:

The clean dist files can be found in your Niagara4 $system_home directory, or in your Niagara 4 image files under the cleanDist directory or in the overlay\cleanDist directory.

Open the .dist file for your JACE's platform using a zip utility like 7-Zip and extract the zip/n4clean.tar.gz file. Also, extract the dev/shmem/n4-xxx.image file, where xxx will be different, depending on the JACE's platform type.

  • JACE 300 ... qnx-jace-n4-npm3xx-etfs2048-clean.dist
  • JACE 600 ... qnx-jace-n4-npm6xx-etfs2048-clean.dist
  • JACE 600E ... qnx-jace-n4-npm6e-etfs2048-clean.dist
  • JACE 603 ... qnx-jace-n4-npm6e-etfs2048-clean.dist
  • JACE 645 ... qnx-jace-n4-npm6e-etfs2048-clean.dist
  • JACE 700 ... qnx-jace-n4-javelina_booke-etfs2048-clean.dist
  • JACE 8000 ... qnx-jace-n4-titan-am335x-clean.dist

Make a Serial Connection to the JACE

The .PDFs in the N4 documentation set describe how to make a serial connection to a JACE in the "system shell" section(s) of each document.

  • Once connected, the controller will boot and display the "login:" prompt.  Enter your Platform credentials.
  • After login, either a "#" or "$" shell prompt or configuration menu similar to the following is shown.
  System Shell
-------------------------------------------------------------------------
  hostid: [unique to your JACE]
  serial number: [unique to your JACE]
  build version: 4.1.25.1.2
  build date: built on 2015-10-07 19:04:59
  system time: Thu Jan 14 16:33:18 UTC 2016
  niagara daemon port: 3011
 
  dm0:  inet 192.168.1.140 netmask 0xffffff00 broadcast 192.168.1.255
        inet6 fe80::5272:24ff:fe9c:55ba%dm0 prefixlen 64 scopeid 0x2
  dm1:
-------------------------------------------------------------------------
 
  1.  Update System Time
  2.  Update Network Settings
  3.  Ping Host
  4.  Enable/Disable SSH/SFTP
  5.  Change Current User Password
  6.  Change System Passphrase
  7.  Enable Front Panel USB
  8.  Configure WIFI
  9.  Reboot
 
  L.  Logout
 
  Enter choice:

  System Shell
-------------------------------------------------------------------------
  hostid: [unique to your JACE]
  serial number: [unique to your JACE]
  build version: 4.1.25.1.2
  build date: built on 2015-10-07 19:04:59
  system time: Thu Jan 14 16:33:18 UTC 2016
  niagara daemon port: 3011

  dm0:  inet 192.168.1.140 netmask 0xffffff00 broadcast 192.168.1.255
            inet6 fe80::5272:24ff:fe9c:55ba%dm0 prefixlen 64 scopeid 0x2
  dm1:
-------------------------------------------------------------------------

  1.  Update System Time
  2.  Update Network Settings
  3.  Ping Host
  4.  Enable/Disable SSH/SFTP
  5.  Change Current User Password
  6.  Change System Passphrase
  7.  Enable Front Panel USB
  8.  Configure WIFI
  9.  Reboot

  L.  Logout

  Enter choice:

Verify correct system time and update as needed

The RTC time may not be correct if the unit has been unpowered for longer than the on-board capacitor backup period.

Using menu ... the first item in the menu list allows you to Update System Time.  The current date/time is displayed.
Enter the new date/time in the form YYYYMMDDhhmm[.SS].  Note that entering the seconds is optional.
For example: 201801111420 for 11-Jan-2018 at 8:20am UTC or 8:20am CST.

Enable SFPT

The Secure FTP service is not enabled by default on a JACE.  Enable the SFPT from the menu above or the shell prompt (if required).

Using menu ... the fourth item in the menu list allows you to enable SSH/SFTP.  Enable it now, using port 22.
Once enabled, enter another choice, "sh" (without quotes).  This will give you the "#" or "$" prompt that you need.

If you could not enable from the menu in the step above, manually start by issuing the command tsudo syssh_sshcfg at the shell prompt.   If the command fails, issue the syssh_sshcfg command.  If the command fails again, enter the following ...

$ cd /sys/bin ... then enter
$ ./syssh_sshcfg ... then enter

Image1.png

Transfer the n4clean.tar.gz and OS Image Files using SFTP Client

Using an SFTP client such as FileZilla, transfer the n4clean.tar.gz file previously extracted for the platform from the clean dist file to the JACE's /zip directory.

Image2.png

If the transfer fails with a permissions error, issue the command tsudo chmod 777 /zip at the shell prompt and try it again.

Next, transfer the .image file you extracted from the clean dist file to the JACE's /dev/shmem directory.

Image3.png

Run osupdate

From the login menu prompt, type sh.  This will exit the menu system and enter the shell mode.  At the "#" or "$" shell prompt, issue the command osupdate.  After a short delay, the shell prompt will return.

Reboot the JACE

Finally, reboot the JACE.  This can be done by issuing the command shutdown hf 0 at the shell prompt.  When the JACE restarts, the unit will automatically process the clean dist file.

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 19569
  • DavidKendrick21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore