Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Reassigning Host Server for a SmartX Controller in EcoStruxure Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Reassigning Host Server for a SmartX Controller in EcoStruxure Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • Katha
    Katha
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2558 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Reassigning Host Server for a SmartX Controller in EcoStruxure Building Operation

JonGreen Mentor
‎2019-10-31 08:05 AM

Last Updated: CraigEl Champion ‎2025-10-19 04:44 PM

Issue

When migrating a SmartX Controller (e.g., MP-C, MP-V, RP-C, IP-IO) from one Automation Server to another within the EcoStruxure Building Operation platform, you may encounter the following error:

The following devices appear to be hosted by another server. In order to host them, you must first right click the device and select "Clear host information"

 

2019-10-31_10-29-02.png

This happens because SmartX devices are designed to be hosted by only one Automation Server at a time.

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation Automation Server (AS-B, AS-P)
  • Multi-purpose Controllers (MP-C, MP-V)
  • Room Controllers (RP-C)
  • IP-IO Modules

Cause

SmartX Controllers maintain persistent host binding metadata. When a controller is discovered by a new Automation Server,  it checks for existing host assignments. If the controller is still linked to a previous Automation Server, the system prevents reassignment to avoid conflicts in device management and communication.

Resolution

  1. 1. Open Device Discovery

    • In WorkStation, navigate to the Device Discovery tab of the target Automation Server.

    2. Locate the SmartX Controller

    • Initiate a BACnet device scan.
    • The controller will appear flagged as hosted by another server.

    3. Clear Host Information

    • Right-click the detected controller.
    • Select “Clear Host Information” from the context menu.2019-10-31_10-33-45.png
    • This removes the previous host binding.

    4. Re-host the Controller

    • Add the controller to the new Automation Server’s configuration tree.
    • Proceed with commissioning as usual.

Best Practices

  • Always ensure the previous Automation Server is offline or has released the controller before reassignment.
  • Use consistent naming conventions and documentation to track controller assignments.
  • Perform backups before making host changes to preserve configuration integrity.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • Clear host information
  • JonathanGreen19
  • KatharineVasquez25
  • Rehosting
  • smartx
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore