Problems installing Vista Webstation 5.1.5 or newer

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Problems installing Vista Webstation 5.1.5 or newer
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1701 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Problems installing Vista Webstation 5.1.5 or newer

Picard Product_Support
‎2018-09-07 07:02 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:54 AM

Issue

Problems installing Vista Webstation 5.1.5 or newer

Product Line

TAC Vista

Environment

  • Vista Webapps (Webstation) 5.1.5
  • Windows 2008 Server 32-bit or 64-bit.

Cause

In order to install TAC Vista Webstation successfully on Windows Server 2008, there are a number of steps and prerequisites to be checked.

Resolution

In order to install TAC Vista Webstation successfully on Windows Server 2008 it has to be done in the following order:

PC Preparation – Only if you can not access the Run as administrator context-menu!

  • Log in as an administrator and create a new administrator group (eg. VistaAdmin) and add a user to this group. By doing this you will be able to access the Run as administrator context menu later on (users added to the Windows administrator group do not always receive full administrator rights).

Install IIS 7 and ASP.net

  • Start the Server Manager (Right-click on Computer in the start-menu or the Computer desktop icon if running classic start-menu and select Manage).
  • Right-click Roles and click Add roles.
  • In the dialogue that opens up click Next and then select Web Server (IIS).

  • In the dialogue that follows click Add Required Features.

  • Click Next (twice).
  • On the select Role services page select ASP.net.

  • In the dialogue window that appears click Add Required Role Services.

  • Click Next and then click Install.

NOTE FOR WINDOWS 7 USERS!

Whilst Windows 7 is not officially supported for running Webstation it may be used in a test environment. It's important to note that the IIS and ASP.net installation is slightly different - the user is not asked to add roles, the user is asked to add windows features (see screenshot below).

Ensure .net framework 4.0 is installed

  • Open Server Manager and select Features.
  • Scroll down and ensure .net framework 4.0 is installed. If not:
  • Open Internet Explorer.
  • From the menu select Tools\Windows Update (Safety\Windows Update in IE8)
  • Run windows update and install .net framework 4.0

Install TAC Vista Server and any hotfixes

Install TAC Vista Webstation and any hotfixes

As administrator, register ASP.Net version 4.0

  • Click on start and then All programs\Accessories.
  • Right-click on Command Prompt and select Runs as administrator.

If using 32-bit:

  • Open explorer and locate the %SystemRoot%\Microsoft.NET\Framework\v4.0.30319\aspnet_regiis.

If using 64-bit:

  • Open explorer and locate the %SystemRoot%\Microsoft.NET\Framework64\v4.0.30319\aspnet_regiis.
  • Ensuring that the directory is set to C:\ copy the file path into command prompt and the add the following text : aspnet_regiis.exe -i -enable
  • Press Enter

Confirm the installation was successful

  • Click on start and then type inetmgr in the search box. This will open IIS manager.
  • Expand the hierarchical menu on the left and then expand the Sites folder.
  • Expand Default Web Sites and select Webstation
  • Right-click on webstation and select manage application > Advanced Settings.
  • In the Application Pool field it should say SE ASP.NET v4.0 Classic

All that is left now is ISAPI, CGI (see "HTTP Error 404.2 - Not found. The page you are requesting cannot be served because of the ISAPI and...) and DCOM settings (see TAC Vista Installation Manual or Helpful Vista Utilities - Configure DCOM instantly, Register ASP.NET).

License problem: Webstation - No license Available

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4765
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore