Page links do not work in Webstation but work in Workstation
  • Page links do not work in Webstation but work in Workstation
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • PeterLarsen
    PeterLarsen
‎2018-09-11 02:50 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:38 PM
Webstation TGML links used to navigate between Graphics pages do not work.
These TGML page links work in workstation
SmartStruxure
The name of the Enterprise Server database has an illegal character. A sample of this would be if the Enterprise Server is named "Server'1"
The ( ') affects the HTTP application and prevents the page links from working.
Although the name is accepted and works in Workstation, WebStation does not allow this character. This will be corrected in a later revision.
The only resolution at this stage is to rename the Enterprise Server to a name with valid characters.
If there are Automation Servers already installed under the Enterprise Server then there is a major issue with renaming the Enterprise Server and we would not recommend renaming you servers unless you are in the early stages of your project.
  • You will need to detach and delete all of the Automation Servers and then Rename the Enterprise Server.
  • Bindings will be lost in this process and will need to be recreated when the Automation Servers are added back in.
See Illegal object name characters in StruxureWare Building Operation.