Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Offline monitoring of a Zigbee device in EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Offline monitoring of a Zigbee device in EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RandyDavis
    RandyDavis
  • Jonas_Brissman
    Jonas_Brissman

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1635 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Offline monitoring of a Zigbee device in EBO

Janeway Jonas_Brissman Janeway
‎2022-02-16 12:32 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-02-16 04:27 PM

Issue

How to create an offline alarm if the AS-P or RP-C loses the connection to a Zigbee sensor (SED-MTH-G-5045, SED-WDC-G-5045, and SED-WLS-G-5045) connected to AS-P or RP-C.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium (AS-P)
  • Building Operation Room Controller (RP-C)
  • Greenpower sensors SED-CO2-G-5045 and SED-TRH-G-5045
  • non-Greenpower sensors SED-MTH-G-5045, SED-WDC-G-5045, SED-WLS-G-5045

Cause

The Zigbee device will communicate the measured data with a time interval, if EBO doesn't hear the data it should mark the device as offline and generate an offline alarm

Resolution

In general, the RP-C or AS-P will listen for communication from the Zigbee device and if it doesn’t hear any communication for a certain time period, the Offline timeout (which can be specified in the properties for the Zigbee device in EBO) will set the device offline and an offline alarm will be displayed in the alarm list.

2022-02-15_14-44-24.jpg

How often the Zigbee device will communicate the measured data depends on the Zigbee device.
It is possible to see and configure how often it should send the data in EBO but depending on the device it can be found in different places in EBO.

For the Greenpower sensors SED-CO2-G-5045 and SED-TRH-G-5045 it is found here:

2022-02-15_14-32-37.jpg

The default value can be found in the specification sheet for the sensor.

And for the non-Greenpower sensors SED-MTH-G-5045, SED-WDC-G-5045, SED-WLS-G-5045
It can be found here:

 2022-02-15_14-35-37.jpg

It is possible to change the interval for how often the sensor will send the data but this may cause the battery in the sensor to drain faster.

It is recommended that the Offline timeout is set to more than twice the heartbeat interval from the sensor so that it will not be set as offline if only one message from the sensor is missed by the RP-C or AS-P.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • JonasBrissman22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.