Issue
Use the block DI to monitor an IO module, and generate an alarm when it is offline. But the above-mentioned function cannot be realized.
Product Line
TAC Vista
Environment
- Menta
- Xenta 301, 302, 401
- Xenta I/O Modules
Cause
If there is a configuration error in block DI, the right alarm cannot be generated. It is necessary to check and correct the configuration error.
Resolution
Create and configure the block DI and Alarm block according to the following procedure, then the IO ...