Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Monitoring an IO module online status and how to generate an alarm when it is offline

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Monitoring an IO module online status and how to generate an alarm when it is offline
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • Zhenting_HU
    Zhenting_HU
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3170 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Monitoring an IO module online status and how to generate an alarm when it is offline

Picard Product_Support
‎2018-09-10 11:57 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:19 PM

Issue

Use the block DI to monitor an IO module, and generate an alarm when it is offline. But the above-mentioned function cannot be realized.

Product Line

TAC Vista

Environment

  • Menta
  • Xenta 301, 302, 401
  • Xenta I/O Modules

Cause

If there is a configuration error in block DI, the right alarm cannot be generated. It is necessary to check and correct the configuration error.

Resolution

Create and configure the block DI and Alarm block according to the following procedure, then the IO module status can be monitored. When it is offline, an alarm will occur in the alarm window in TAC Workstation.

 

1. Create a block DI. (See the Figure 1)

Figure 1

2. Edit the block DI and input DI identifier such as the monitored module name, Status_411 in instance. (See the Figure 2)

          Figure 2

3. Click BIND in Edit window, select the Online Device in BIND TO column, and input the IO module number in DEVICE ADDRESS. (See the Figure 3)

              Figure 3

4. The module number can be found in IO Expansion and Wall Module Table of DEVICE SPECIFICATION in Menta Options toolbar. In the under instance picture, the M1 module, TAC Xenta 411, its device address is 1; the M2 module, TAC Xenta 421A, its device address is 2; and so on, the M5’s device address is 5. (See the Figure 4)

      Figure 4

5. After creating and configuring the block DI, the block Alarm should be created. (See the Figure 5)

               Figure 5

6. Then connect the block DI and Alarm. When the IO module is online, the DI value is generally 1. So the block NOT must be used. (See the Figure 6)

        Figure 6

 

You can also reference Monitor the online status of a base unit's associated I/O modules.

Labels (1)
Labels:
  • TAC Vista
Tags (6)
  • Find more articles tagged with:
  • 12167
  • 401
  • menta
  • PeterLarsen22
  • status
  • xenta
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore