Maximum Limits for StruxureWare Lite Design

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Maximum Limits for StruxureWare Lite Design
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MaximeLaudren
    MaximeLaudren
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2263 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Maximum Limits for StruxureWare Lite Design

Picard Product_Support
‎2018-09-11 04:37 AM

Last Updated: Lieutenant MaximeLaudren Lieutenant ‎2022-08-18 09:22 AM

Issue

Maximum Limits for SmartStruxure Lite Design (Scalability, Capacity)

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager (MPM)

Cause

What are the maximum number of communication between managers and end device

Resolution

Guidelines: number of end devices per node
Wired
● 6 wired inputs (Ohms / Volts, Analog or Digital)
● 6 wired outputs (4 analog 0-12VDC, 2 digital) The analog output ports has a maximum nominal load of 50mA each.
● Need more? Modbus I/O extenders, SEC-TE, etc.

Wireless devices
● In theory: almost unlimited (no physical constraints)
● In practice: limited by range and strength of wireless signal
    ● EnOcean: Rule of thumb is within room (up to 75ft in building – line of sight)
    ● ZigBee: Rule of thumb is within room (up to 150ft in building – line of sight)

    Limited by application
    ● Frequency of transmission
    ● Efficient handling of data queues

Guidelines: number of end devices per node
BACnet - with the current basic client capabilities, the maximum number of devices supported on a single BACnet network is 1000.
Modbus
     Limitations for ModBus connectivity per MPM is 31 devices but depends on polling rate and amount of points:
        ● Using pre-defined objects, polling rate is 30s / device
        ● Using Lua script, polling rate variable

ZigBee or EnOcean for the end devices?

ZigBee
● Longer range
● Reliability built-in the protocol (ack, retries, …)
● Requires a battery
● Multiple channels available (possible to isolate networks / groups)

EnOcean
● Self-powered (no battery)
● Easy to deploy
● Lower range
● Reliability must be ensured at the application level
● No retries

● ZigBee coordinator is a device that sets up the network, is aware of all the nodes within its network. Every ZigBee network must contain a network coordinator.
● ZigBee router can act as an intermediate router, passing on data from other devices.
● ZigBee end-device is part of the network, but doesn’t re-route information to neighbors.


How many devices can I use?

ZigBee
● A ZigBee network should not have more than 75 ZigBee devices in total (coordinator, router and end devices);
● A ZigBee network should not have more than 24 ZigBee routers (+1 coordinator)
● A ZigBee node (coordinator or router) should not control more than 10 peripheral end devices.

EnOcean
● Using pre-built objects:
● 4 Thermostats
● 20 Switches
● 20 Relays
● The maximum number of devices added to each MPM is 49
●The maximum number of EnOcean devices added to each MPM is 49
●The maximum number of EnOcean devices with the same EEP added to each MPM is 49 .This only applies to firmware 2.13.1 and later, the limit for previous firmware is 20. An Exception is the following limits for devices/widgets per MPM:
20 EnOcean Switches
20 EnOcean Relays
4 EnOcean Thermostats


The AV and BV variables
The MPM-UN controller comes with 100 AV's and 100 BV's.
MPM has capacity for up to 700 AV's and 700 BV's. After the initial 100 are consumed, add Value Banks of 100 for each AV and BV. Value Banks will be added as sub-devices under the main MPM. 

Maximum data Points: MPMs can have up to 750 data points per monitor.

What is the maximum size for background graphics?
The maximum size of a background picture (in dashboard or section map) is 2Mbyte with a maximum resolution of 1920 x 1080 (Width x Height).

For analog inputs with a signal range in Ohms has no reading limit. You just need to configure the table in the AIC object assigned to referred input.

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (2)
  • Find more articles tagged with:
  • 13963
  • MaximeLaudren22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of