MSTP Network reliability issue after creation via imported XML file
  • MSTP Network reliability issue after creation via imported XML file
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
‎2018-09-11 12:52 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:57 PM
After creating the MSTP network from an imported XML file, all devices under the network are offline and the network is unreliable.
BACnet
The MSTP network number is not included in the XML and must be reset manually.
In the MSTP network property window set the Network ID to the appropriate number.
Note: To bring the devices online see Importing an exported MSTP network back into StruxureWare Building Operation.
  • 17872