Importing an exported MSTP network back into StruxureWare Building Operation
  • Importing an exported MSTP network back into StruxureWare Building Operation
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • AbeMeran
    AbeMeran
  • sesa125819
    sesa125819
‎2018-09-07 09:02 AM
Importing an MSTP network.
Importing
Import
MSTP
Network
Customer had made some identification mistakes in the BACnet Interface configuration, and decided the export the MSTP network, recreate the BACnet interface, and then import the MSTP network back in again.
If the MSTP network is exported, deleted from the tree, and then imported back again, all controllers will show offline.
  • When an MSTP network (and thus the b3 devices underneath it) is exported, we don't export the device ID, MAC ID, or serial number of the devices (they cannot be copied, therefore are non-exportable).
  • When the object set is imported back in, these values are empty.
  • After importing, go to the properties of the MSTP network and put back the Network ID if found to be blank.
  • The simplest way to regain these values is to drag/drop the physical device from the hardware folder to the logical device under the MSTP network. You may need to run a discovery on the MSTP network first to make sure the hardware folder's view of the world is current.
  • Assuming the association of the physical and logical devices is successful, you should only need to download from the AS to the devices, to make them fully operational.