License Violation Alarm Triggered Without License Violation Banner displayed

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • License Violation Alarm Triggered Without License Violation Banner displayed
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
614 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

License Violation Alarm Triggered Without License Violation Banner displayed

Picard RobertAndriolo Picard
‎2025-08-26 02:57 AM

 

Issue

A License Violation alarm is triggered without displaying a License Violation banner.

Alarm reactivates after acknowledgment, approximately every 10 minutes.

RobertAndriolo_0-1756107449099.png

 

RobertAndriolo_2-1756107579695.png

Device Administrator also shows a license violation in "License status," when all servers show no violation.

DA-LicenseViolation.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Enterprise Central
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled

Cause

Potential communication issue, possibly related to return path or port configuration.

An incorrect ES port may be in use, which could be contributing to the issue.

The Communication Tab [Communication View] and Server List in xbk Analyzer show only the ES, indicating limited server visibility.

Resolution

  1. Verify Communication Path

    • Ensure the ES is defined as using the same ports across all servers.
    • Confirm that the ports are correctly configured and open on all relevant servers.
  2. Review the Communication Tab [Communication View] and Server List

    • Check that all expected servers are listed and actively communicating.
    • If only the ES is visible, investigate potential network or configuration issues.
    • See article for additional information: Updating a Enterprise Server IP Address - Schneider Electric Community
  3. Check AS Logs

    • Log in to the Automation Servers to identify any communication errors.
    • These errors may not be visible from the ES alone.

Next Steps

  • If the above steps do not resolve the issue or the root cause remains unclear:
    • Refer to the article for possible communication-related troubleshooting options: Enterprise Server and Automation Server Bindings show Unresolved - Schneider Electric Community
    • Refer to the article for additional license troubleshooting options: Troubleshooting EBO license violation issues - Schneider Electric Community
    • Contact your local support organization for further assistance.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore