Enterprise Server and Automation Server Bindings Show "Unresolved"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enterprise Server and Automation Server Bindings Show "Unresolved"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
23159 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enterprise Server and Automation Server Bindings Show "Unresolved"

Picard Product_Support
‎2018-09-11 03:18 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-05 10:46 PM

Issue

Bindings between:

  • Enterprise Server and Automation Server, or
  • Two Automation Servers

...appear as "Unresolved" in the system.

Unresolved Binding.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • Binding Diagnostics

Cause

This issue is typically caused by:

  1. Incorrect communication configuration
  2. Firewall or antivirus blocking communication
  3. Port conflicts or usage by other applications
  4. Network adapter misconfiguration
  5. Unsupported architecture (e.g., EC and ES on same PC)

Resolution

🔒 1. Firewall Configuration

  • Ensure Windows Firewall is correctly configured:
    • Use the Firewall Config Tool to set inbound/outbound rules.
    • Refer to: Creating Windows Firewall Rules for Building Operation.
  • If unsure, temporarily disable the firewall to test connectivity.
  • Watch for network profile switching (Private ↔ Public) during commissioning.

⚠️ Even if ASs appear online, unresolved bindings may still occur due to firewall issues.


🧩 2. Special Character in Server Name

  • For v1.4 or v1.5 servers with an ampersand (&) in the name:
    • Request hotfix:
      • v1.4: R1.4.1.16201 or later
      • v1.5: R1.5.0.1601 or later

🌐 3. Network & IP Configuration

  • Confirm ES IP address matches the PC’s active NIC IP.
    • If not, follow: How to Set the Enterprise Server IP Address.
  • Use IP address instead of domain name if DNS resolution is unreliable.
  • Ensure all required ports are open between ES and AS.
    • Refer to: Information Technology System Planning Guide → Search “Network Ports”.
  • Disable unused network adapters (e.g., Wi-Fi, VMware, VirtualBox).
    • ES should use the primary NIC.

🔄 4. Repair Communication

  • Right-click the ES → Advanced > Repair Server Communication
    • This refreshes the communication tables.
  • Detach and re-add ASs to the ES if needed.
    • See: Unable to Add an Automation Server Underneath an Enterprise Server.

🛡️ 5. Antivirus & Security Software

  • Disable network monitoring features in antivirus software.
  • For Schneider laptops:
    • Right-click Trellix in system tray → Enable Firewall Timed Groups.

      Trellix Timed Groups.png


⚠️ 6. Unsupported Architecture

  • Enterprise Central (EC) and Enterprise Server (ES) should not run on the same PC with default ports.
    • If testing:
      • Stop EC service or
      • Reconfigure ports to avoid conflicts.

        EC and ES Installed with Defaul Settings.png


🔍 Additional Tips

  • Use the Communication tab on each server to verify peer visibility.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (8)
  • Find more articles tagged with:
  • 16547
  • ampersand
  • blue
  • CraigEllis25
  • DavidChild19
  • HernanUruena23
  • HernanUruena24
  • triangle
Was this article helpful? Yes No
67% helpful (6/9)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore