It is not possible to get a Xenta Server or 911 online in TAC Vista.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • It is not possible to get a Xenta Server or 911 online in TAC Vista.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • Jonas_Brissman
    Jonas_Brissman
  • sesa150555
    sesa150555
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2355 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

It is not possible to get a Xenta Server or 911 online in TAC Vista.

Picard Product_Support
‎2018-09-06 03:53 PM

Last Updated: Picard RobertAndriolo Picard ‎2022-12-01 06:12 PM

Issue

Not possible to get a Xenta Server / 911 online in TAC Vista.
It is possible to ping it and connect to it via a Web browser using ports 443, 80, and Port 1068 is open, but it is not possible to get online in Vista.

Product Line

TAC Vista Server

Environment

  • TAC Vista
  • TAC Xenta 911
  • TAC Xenta Server

Cause

The problem, in this case, was that another Vista server was connected to the Xenta Server / 911. 
This could have been from a technician or the customer who started Vista with this database loaded and had the device online in their Database.
The Xenta Server / 911 will only communicate with one Vista Server at a time and will close the connection if another Vista tries to communicate with it. 

 

Using Wireshark it is possible to monitor this scenario as shown below: 

  • Packet number 57439: Vista is trying to establish communication with the Xenta Server or 911( sending an SYN).
  • Packet number 57440: The Xenta sends an acknowledgment on the SYN from Vista, but with the window size set to zero, this is because the Xenta can't buffer information as a computer does.
  • Packet number 57441: Vista  sends an acknowledgment on the message from the Xenta
  • Packet number 57448: The Xenta sets the correct window size.
  • Packet number 57449: Vista starts to communicate
  • Packet number 57452: The Xenta closes the communication to the Vista server 

Resolution

Ensure only one Vista server is started when the Xenta server / 911 is included in the database.

Labels (1)
Labels:
  • TAC Vista
Tags (8)
  • Find more articles tagged with:
  • 7763
  • offline
  • PeterLarsen22
  • shark
  • wire
  • wireshark
  • xenta731
  • xentaserver
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore