Increasing data update rates for an IC3 Modbus controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Increasing data update rates for an IC3 Modbus controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • David_Kendrick
    David_Kendrick
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1360 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Increasing data update rates for an IC3 Modbus controller

Picard Product_Support
‎2018-09-06 01:50 PM

Last Updated: Admiral David_Kendrick Admiral ‎2022-08-09 09:03 AM

Issue

The time taken for values to change on a Sigma client is a lot slower then the change of values for the Modbus devices, how can this be sped up?

Product Line

Satchwell Sigma

Environment

  • Sigma Modbus
  • RS-232
  • RS-485
  • TCP502

Cause

Modbus protocol is a polling type and configuration changes to default settings can be made to speed up data collection for the IC3 Modbus controller.  

Resolution

There are changes that can be made to default settings that can allow the IC3 Modbus to collect data at a quicker or a more efficient way.  It should be noted that these changes can be counter productive and should not be applied without careful thought to the consequences.  That is, the third party Modbus device may not respond quickly enough for the IC3 Modbus request and therefore cause a retry, particularly on RS485 LANs.

1. For RS485/232 communications LAN it is important to check the LAN installation is correct.  See Investigating Modbus devices shown as offline in Sigma particularly if Modbus controllers are going offline. 

Note:  Modbus is a polling protocol and failures and subsequent retries will slow down the update rates for those devices online.

2. Changes to the IC3 Modbus gateway.txt file;

    a) Increase baud rate

; Default Baud Rate (e.g. 1200)
9600

If the third party device (RS485) supports it, the baud rate can be increased.  But, if the communications environment is poor then reducing may be the better alternative.

   b)  Retry counters and timers

; RTU message separation time
18

-  The delay to the next IC3 Modbus request following a previous reply.  Should be increased to 200 or more to prevent timeout

; Retry Check Period
1

- Time in seconds after a failure. Suggest 1 second

; Number Of Retries
3

- Number of times to perform a retry before moving on to the next register.  Suggest 3.

; Device Reset Interval
0x01

; Device Down Interval
0x01

 - Set to 0x01 is the retry time once a failure has occurred and before the next time it will attempt device again (0x01 = 60 seconds)

   c) Delay between controllers

In the body of the mapping table the 5th field is the minimum time before polling the same device and can be set to zero

31,2,3,0,1,0x0007,0,0,1

   d) Up to 7 consecutive Modbus registers can be read simultaneously

In the body of the mapping table the 6th field is the number of consecutive fields to be read.  This can be increased up to 7, but both the Modbus register numbers and Sigma object numbers must be consecutive

31,2,3,0,1,7,0,0,1  ;ModBMS Test2 40001
38,2,3,7,1,4,0,0,1  ;ModBMS Test2 40008

3. Changes to the Sigma objects.  Note: these changes do not affect the Modbus update rate but can increase the displayed or graphic update rate.

     a) Scan priority number decrease

Selected Sigma objects can have there Scan Priority decreased or those Sigma objects that do not update as quickly increased allowing the IC3 Modbus controller to process the critical objects more often

     b) Tolerance value - particularly for Graphic, Dynaview and Actipane displays

Modify the Sigma object tolerance to match that of the object value.  See Sigma graphic only updates when first opened and no regular updates occur there after

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 5261
  • DavidKendrick22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of