I/NET Configuration profile editor does not startup

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Configuration profile editor does not startup
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1786 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Configuration profile editor does not startup

Picard Product_Support
‎2018-09-07 06:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:33 PM

Issue

After configuring an I/NET workstation to connect as a Remote Client the I/NET Configuration profile editor does not start.

INetCfg.exe appears in the Windows Task manager processes but no application user interface (GUI) is displayed.

Product Line

TAC INET

Environment

I/NET Seven 2.13 and above configured as Remote Client

Cause

I/NET Configuration profile editor attempts to connect to its active profile database server, if this is not active it will sit and wait for the database server to become active before displaying the I/NET Configuration Profiles user interface (GUI).

Resolution

It is possible to change the default (or active) profile, provided you have more than one configuration profile.  This is achieved by changing the following settings in the registry.

If you only have one profile on your I/NET workstation, you could export a known working profile from another I/NET workstation.  Refer to the following Exporting/Importing Configuration Profiles for the procedure to do this.

Ensure that the INetCfg.exe application is not running in the processes, if it is then use the Windows Task Manager to check and end the process before proceeding with the following steps:

  1. From the Windows Start menu select RUN
  2. Enter in the command regedit
  3. Locate the Registry Key > HKEY_LOCAL_MACHINE> SOFTWARE> CSI - Control Systems International> I/Net 2000> Configurations>
    1. In this container (Configurations) there is String named "Active" this should display the name of the active profile been used by I/NET.
    2. Edit this string to another profile that exists, typically the initial profile called "Config1" is the safest.
    3. Close the Registry Editor
  4. Run up I/NET Configuration – the profile editor should now start and display the Active configuration you selected above.
  5. Modify the profile you wish to use
  6. Ensure that the Database Server name is now local to your machine name or is online.
    1. If not you can edit this my selecting the Connection Button within the profile. 
  7. Make any necessary changes required to the profile
  8. Select OK.
  9. Ensure the profile you modified is now made active
  10. Close the I/NET Configuration Profiles editor and I/NET is now ready to run.
Labels (1)
Labels:
  • TAC INET
Tags (3)
  • Find more articles tagged with:
  • 4671
  • INet Config does not start
  • Remote Client
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore