Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

How to use the Continuum BACnet point attribute COV Increment

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to use the Continuum BACnet point attribute COV Increment
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • sesa101527
    sesa101527

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4318 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to use the Continuum BACnet point attribute COV Increment

Picard Product_Support
‎2018-09-06 02:59 PM

Last Updated: Administrator CraigEl Administrator ‎2022-09-12 06:50 PM

Issue

What is the BACnet attribute COV Increment and how to use it

Product Line

Andover Continuum

Environment

BACnet

Cause

The COV Increment attribute on a BACnet point is equivalent to the Threshold attribute of standard Continuum Infinity inputs. When a Continuum BACnet point is subscribed to by other BACnet devices using COV (Change of Value), its value must change by at least that COV Increment value before a new Value Notification will be sent out. Using this attribute will decrease network traffic especially on the MSTP network when subscribing to frequently changing values. 

Resolution

This CovIncrement attribute can be set in the BACnet point's Editor on the Basic Alarms Tab.

 

If you have a CyberStation prior to Version 1.8, setting this value from the point editor will not stay persistent in the controller after the controller is reloaded, it will default to 0. In order to keep the value after a reload, you will need to write a PE program to set the desired value after a reload. The program should be Autostart and Fallthru.

A sample of the program is below:

Line SetCov
Writeproperty("Full Bacnet Path to Point", CovIncrement, "Desired Value")
Stop

If you have several points that need the CovIncrement set, you would just add the additional lines into this program.

 

In 1.8 or greater, this program is not needed as these attributes get sent to controller on a reload. Suitable initial CovIncrements still need to be added to each BACnet point however as they default to 0.

Labels (1)
Labels:
  • Andover Continuum
Tags (3)
  • Find more articles tagged with:
  • 2557
  • DavidKendrick22
  • retained
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore