How to truncate event tables in Continuum databases

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to truncate event tables in Continuum databases
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4998 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to truncate event tables in Continuum databases

Picard Product_Support
‎2018-09-07 03:43 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:38 AM

Issue

How to truncate event tables in Continuum databases.

Product Line

Andover Continuum

Environment

  • Continuum 1.xx
  • SQL 7
  • SQL 2000
  • SQL 2005

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

Stand Alone Continuum Databases use Microsoft MSDE and SQL Express databases which have size limitations. Once these databases reach full capacity they will need to have data truncated from tables to try and reduce the size of the database. Databases should never exceed their size limitations, but if they do, reducing the size of some of the tables will in most cases allow the database to be functional again.

Microsoft SQL MSDE database size limit is 2 gig

Microsoft SQL Express database size limit is 4 gig

Resolution

Once logged into the SQL MSDE or SQL Express database, the queries below will reduce the size of the database.

As with any database, make sure you backup the database before running any queries.

The Usernames and Passwords used below are defaults, your UN/PW may differ.

To log into SQL MSDE use the following commandline.

osql -Usa -P

To log into SQL 2005 Express us the following commandline with your servername

sqlcmd -Sput_server_name_here\sqlexpress -Usa -Padminadmin

Once logged in you'll be prompted with a 1> at which time you'll change the context of the database you'll be truncating information on. For example if your database name is ContinuumDB you would use the following.

1>Use ContinuumDB

2> Go

1>Now put in one of the queries below

2> type in Go to execute

/****** Replace 90  with the number of days to maintain in each log ********/

delete from accessevent where DATEDIFF(day, timestamp, getdate()) > 90

delete from activityevent where DATEDIFF(day, timestamp, getdate()) > 90

delete from alarmevent where DATEDIFF(day, timestamp, getdate()) > 90

delete from errorevent where DATEDIFF(day, timestamp, getdate()) > 90

** To gain back the space after deleting rows
SQL Express
Right click on Continuumdb>Tasks>Shrink>Database

MSDE(osql)
 dbcc shrinkdatabase ('your_database_name',0) (enter)
go (enter)

dbcc shrinkdatabase ('your_database_name',0) (enter)

go (enter)

 

To truncate from the Full SQL server or SQL Express non command line interface, see Removing unwanted entries from an Alarm log, Access Event log, Error log, and Activity log automatic....

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4289
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore