How to show damper feedback for an i2/b3 866-V

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to show damper feedback for an i2/b3 866-V
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3030 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to show damper feedback for an i2/b3 866-V

Picard Product_Support
‎2018-09-06 08:17 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:58 AM

Issue

Existing documentation for showing damper feedback and provide damper calibration is applicable only for Continuum and the same steps will not work in SmartStruxure.

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure
  • i2866-V
  • b3866-V

Cause

Damper feedback and calibration for these controllers do not work the same in SmartStruxure as they do in Continuum.

Resolution

The correct damper feedback can be shown, but will require a script program to correctly calculate this and then write this back to an Analog_Value.

Unfortunately, it is not possible to bind directly to the "LCD State" attribute to be able to toggle this (and the damper calibration feature) from within a Script Program. For now, toggle this attribute of the Damper Output manually from "enabled" to "disabled" and back. This will set the damper to drive closed fully, then open fully, then to about 75%.

After this is calibrated properly the "Override Value" attribute in the Damper Output will update with likely a very large and strange-looking number. To convert this to something usable, multiply this value by 100 to give a percentage open value. See Zip file with XML code and screenshots of the configuration with notes.

Either import supplied XML file into b3866-v or create below objects:

  1. Create DamperOutput as a multistate output. Assign to channel 1.
  2. Create DamperPos AnalogValue.
  3. Create Script Program Damper_Position and input code as shown in image. This will be a looping program.
  4. Bind DamperOverrideValue to the OverrideValue attribute of the Damper Output and DamperPosition to the DamperPos AnalogValue we created earlier. See image for details.

After the points and program is created and the damper calibrated, you should see the DamperPos AnalogValue update with a live representation of the current Damper Position.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
b3866-v_DamperPos_Script.zip
Tags (9)
  • Find more articles tagged with:
  • 19001
  • b3866
  • damper
  • DavidChild21
  • feedback
  • i2866
  • PaulFrost21
  • position
  • vav
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore