How to set EcoStruxure BMS Server as Modbus TCP Server or Modbus RTU Server (Slave)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to set EcoStruxure BMS Server as Modbus TCP Server or Modbus RTU Server (Slave)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • PeterLarsen
    PeterLarsen
  • DavidFisher
    DavidFisher
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
5 Likes
13786 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to set EcoStruxure BMS Server as Modbus TCP Server or Modbus RTU Server (Slave)

Picard Product_Support
‎2018-09-06 09:26 AM

Last Updated: Administrator CraigEl Administrator ‎2022-12-08 05:20 PM

Issue

A 3rd party system wants to poll data from EcoStruxure BMS server through Modbus, how to set it up?

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Enterprise Server

Cause

If an EcoStruxure BMS server needs to share data with a 3rd party system through Modbus, the EcoStruxure BMS server can act in one of two roles: Modbus TCP server or Modbus RTU Server (Slave)

EBO server acting as RTU slaveEBO server acting as RTU slaveEBO server acting as Modbus TCP serverEBO server acting as Modbus TCP server

 

Resolution

  1.  Create a Modbus interface under the EcoStruxure BMS server and define the Modbus device ID for the EcoStruxure BMS server.
  2. Create Modbus points under this Modbus interface and set the register numbers and register type for the points.
  3. Create a Modbus Slave network for serial connection, select the COM port and set relative communication parameter. Or create a Modbus TCP Server for TCP connection and can change the default Modbus TCP port if needed (Usually just leave it as default).
  4. Use standard Modbus test software like Modscan to scan the points through TCP or serial.
    1. Use Function Code 1 or 2 to read Digital Modbus points and Code 3 or 4 for Analog Modbus points.
    2. Be sure to match the data length setting in Modscan with the real points number in the EBO server. For instance, if there are only 3 values in EBO Modbus interface, the data length setting must be less than 3 in Modscan. Or it will show error in Modscan.

The below video will demonstrate how to configure EcoStruxure BMS server to act as Modbus TCP server or Modbus RTU slave


 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 16692
  • HernanUruena23
  • HernanUruena24
  • MahmoudSayed22
  • PeterLarsen22
Was this article helpful? Yes No
67% helpful (16/24)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore