How to set Alarm Window to Pop up on Alarm
  • How to set Alarm Window to Pop up on Alarm
  • Katha
    Katha
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-11 07:27 AM
Last Updated: Administrator CraigEl Administrator ‎2025-10-12 10:01 PM
The alarm window either does not display or unexpectedly displays when an alarm is triggered.
Building Operation Workstation
The Alarm View Properties are not configured correctly, which affects whether the alarm window pops up upon alarm activation.
For Versions older than 3.2.x:
  1. Right-click inside the Alarm View window.
  2. Select Alarm View Settings > Properties.
  3. Locate the Display on Alarm property.
  4. Set it to the desired state (True or False).
For Version 3.2.x and above:
  • This feature is controlled via the “Display on Alarm” setting on the alarm object's Attachment tab.
  • Enable or disable it based according to requirements. Katha_0-1760330536111.png
Tags (3)