Issue
The alarm window either does not display or unexpectedly displays when an alarm is triggered.
Product Line
EcoStruxure Building Operation
Environment
Building Operation Workstation
Cause
The Alarm View Properties are not configured correctly, which affects whether the alarm window pops up upon alarm activation.
Resolution
For Versions older than 3.2.x:
- Right-click inside the Alarm View window.
- Select Alarm View Settings > Properties.
- Locate the Display on Alarm property.
- Set it to the desired state (True or False).
For Version 3.2.x and above:
- This feature is controlled via the “Display on Alarm” setting on the alarm object's Attachment tab.
- Enable or disable it based according to requirements.