How to remove "loose" Areas from Personnel objects that have Areas assigned with a Template
  • How to remove "loose" Areas from Personnel objects that have Areas assigned with a Template
  • AdamSteele
    AdamSteele
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
‎2018-09-06 09:01 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:59 PM
The Area schedule assignments from "Loose" Areas (ones that are individually attached to the Personnel object) can interfere with those assigned through a Template.
Andover Continuum
  • Continuum Access Control
  • Cyberstation
Wish to remove the "loose" Areas so that those assigned by the Template take over.
Here are two methods to do this that will resolve this issue.
  1. For large numbers of affected Personnel, use the Personnel Import Utility for this by removing the areas you do not want from the import file. You may need to re-apply the template you want after this as well. See How to conditionally assign areas to personnel objects using the Personnel Input Utility XSLT transf... that describes this method.
  2. For smaller numbers of Personnel the manual method may be better. For each Personnel object.
    1. Clear out template assignment. Save the object.
    2. Remove all Areas left assigned. Save the object.
    3. Re-assign the previous template. Save the object.
  • 18246