How to program a camera window to pop up when two inputs are True.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to program a camera window to pop up when two inputs are True.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • AdamSteele
    AdamSteele
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2236 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to program a camera window to pop up when two inputs are True.

Picard Product_Support
‎2018-09-10 10:15 AM

Issue

Require details on how to setup two inputs to pop up a camera window when both inputs are True.

Product Line

Security Expert

Environment

Security Expert

Cause

Unsure how to setup programming for two inputs to display video from one camera when both inputs are set to true.

Resolution

Need to create:

  • 3x Virtual Outputs
  • 1x Programmable Function
  • 1x Input Type
  • 1x Area
  • 2x Inputs
  • 1x Event Filter
  • 1x Action

 

Instructions:

Virtual Outputs

  1. Under Programming | Outputs create three (3) new outputs.
  2. Set Module Type to "Output (PX)"
  3. Set module address to "31" or greater.
  4. Set Module Output to "1", "2" and "3" respectively.
  5. Save the changes.

 

Programmable Function

  1. Under Automation | Programmable Functions create a new Programmable Function.
  2. On General tab select Type "Logic Control".
  3. On "Logic Control" tab select Logic Function Mode "7 - Follow Logic AND".
  4. First Output To Check, your first created output.
  5. Second Output To Check, your second created output.
  6. Output To Control, your third created output.
  7. Save the changes.
  8. Right click the new Programmable Function you just created and select "Start".

 

Input Type

  1. Under Programming | Input Type create a new Input Type.
  2. On Options (1) tab select Generate Alarms, Generate 24HR Alarms.
  3. On Options (3) tab select Activate Inout Control Output On Alarm, Deactivate Input Control Output On Restore.
  4. Save the changes.

 

Area

  1. Under Programming | Areas create a new Area.
  2. Important: Ensure this Area is always armed.
  3. Save the changes.

 

Inputs

  1. Under Programming | Inputs create your two inputs (or edit two existing inputs).
  2. On General tab set the Control Output of your first input to the first virtual output you created earlier, the second input to the second virtual output.
  3. On First Assigned Area, Areas and Input Types tab set Area to the area created previously, Input Type to the Input type created previously.
  4. Save the changes.

 

Event Filter

  1. Under Events | Event Filters create an Event Filter.
  2. On Event Types tab unselect "Include All Event Types" and add "Output On By Programmable Function" (both of the options) that show under All Output Events.
  3. On Record tab Add a new record. Select Device Type to be "Output", Controller to your controller, then select the third virtual output you created and press "Add".
  4. Save the changes.

 

Action

  1. Under Events | Actions create a new Action.
  2. Set Type to "Popup Camera Window".
  3. Set Event Filter to the event filter you created earlier.
  4. Set Popup Camera to "Select Camera from List".
  5. Set Camera to the camera you want to show video from.
  6. Save the changes.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • 19458
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of